    Question need help trouble in THERMOKING SB21O reefer



    Is their anybody can help me in solving are problem with thermoking trailer.The problem is we cannot increase the discharge pressure to 275 psi and the liquid refrigerant is not visible in the sight glass in the liquid receiver that is should be.I already do the following change expansion valve,check 3 way valve for defrost,check-valve,bypass valve,charge with right amount of refrigerant,check the suction pressure,try to cover the condenser grille with cardboard and check the compressor all are working well but still it doesn't do anything.I try to swap the compressor to our other unit just to be sure that there is no problem with the compressor it runs okey.This start when I repair leak in the oil return pipe of the compressor then charge it with refrigerant R404a which is made from china.Is there any possibility that this refrigerant causing the problem.



  2. #2
    Join Date
    May 2006
    Location
    India
    Age
    74
    Posts
    399
    Rep Power
    18

    Re: need help trouble in THERMOKING SB21O reefer

    What is the suction pressure ?

  3. #3
    Join Date
    Dec 2007
    Location
    U.A.E
    Posts
    14
    Rep Power
    0

    Re: need help trouble in THERMOKING SB21O reefer

    The suction pressure in the service valve is 70psi upon start up and goes down to 20psi as soon the box cool down.Below the throttelling valve is 20psi this mechanism maintaining this pressure before it goes to the compressor.Do you have any idea that you can share with me

  4. #4
    Join Date
    Apr 2008
    Location
    phillippines
    Posts
    125
    Rep Power
    17

    Re: need help trouble in THERMOKING SB21O reefer

    ruben,

    At 20 psi and a refrigerant of R404 what is the box temp.what is your discharge pressure?

    regards,
    abet

  5. #5
    Join Date
    Dec 2007
    Location
    U.A.E
    Posts
    14
    Rep Power
    0

    Re: need help trouble in THERMOKING SB21O reefer

    Thanks for replying we already solve the problem.It is cause by the Refrigerant we use thats is made in china and without brand name.Right now it is working well the box temp. is -25 c suction is 13-18 psi and the discharge is 275-300 psi.We use dupont Suva 404a.So dont use refrigerant that is made in chain and without brand name it will cause you a problem

Similar Threads

  1. Replies: 12
    Last Post: 27-03-2011, 04:12 AM
  2. Help cutting open 40ft reefer, we now have problems
    By adrian_uk17 in forum Industrial
    Replies: 50
    Last Post: 28-11-2010, 08:11 AM
  3. Replies: 10
    Last Post: 13-06-2008, 05:57 AM
  4. Phoenix Carrier Reefer Unit Trouble
    By razorback76 in forum Trouble Shooting
    Replies: 4
    Last Post: 11-07-2006, 07:39 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •