    Question LG Floor standing 3 Phase Units



    Help!

    We have 2, 3 Phase floor standing LG Air conditioners. Model No: TP-H808FLA0 (85,000 BTU). Due to the high temperatures we experience here, we loss electrical power very often. Of course both A/Cs switch off when the Electgrical Power fails. Once the power is restored, we have to manually switch on both units. Is there anyway, that the units can start automatically when the Electrical Power is restored ?

    Any suggsetions would be helpful.


    Thanks in Advance

    Regards


    Kilo



  2. #2
    Join Date
    Oct 2008
    Location
    mallorca, spain,
    Age
    75
    Posts
    768
    Rep Power
    19

    Re: LG Floor standing 3 Phase Units

    hi , yes the manufactorers , are the people to advise you , basicly you have to identify which phase, is the controle phase< red yellow or blue< and put a fused link from the incoming supply onto the main contactor , so in effect as soon as the mains come back on the contactor comes in< you may want to add a timer<to stop comp, coming streight in
    but do contact the manufacorers

  3. #3
    Join Date
    Nov 2006
    Location
    At home
    Posts
    181
    Rep Power
    18

    Re: LG Floor standing 3 Phase Units

    Quote Originally Posted by sedgy View Post
    hi , yes the manufactorers , are the people to advise you , basicly you have to identify which phase, is the controle phase< red yellow or blue< and put a fused link from the incoming supply onto the main contactor , so in effect as soon as the mains come back on the contactor comes in< you may want to add a timer<to stop comp, coming streight in
    but do contact the manufacorers
    would this not be a very bad idea as you would be taking out any control the system has? how would contactor ever de-energise? what about control circuit? h/p,l/p to name but a few?? what if indoor fan wasnt running? im sure this would create major system life and safety errors!!

    am i missing something?

  4. #4
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: LG Floor standing 3 Phase Units

    Yes..... you don't live in Mallorca.

  5. #5
    Join Date
    Oct 2008
    Location
    mallorca, spain,
    Age
    75
    Posts
    768
    Rep Power
    19

    Re: LG Floor standing 3 Phase Units

    no skywalker , you are not missing anything , I wasent giving a wiring diagram , just giving the guy an idea of a way to turn on his units after a power cut like I said twice < if you read it< ask the manufaterers<
    and yes it is done on mallorca

  6. #6
    Join Date
    Aug 2008
    Location
    Baltics
    Age
    62
    Posts
    786
    Rep Power
    16

    Re: LG Floor standing 3 Phase Units

    Make a try to supply one of PCBs by independent voltage from an UPS (only "electronics" - the "power" part should be fed from the main supply).
    But at first try to find out (e-mail LG) whether there may be some settings with your model for automatic reset. And study please your user manual once more thoroughly .

Similar Threads

  1. Vrv
    By tgoonter in forum Air Conditioning
    Replies: 4
    Last Post: 11-01-2011, 06:25 AM
  2. generic single phase contactor?
    By paul_h in forum Electrical
    Replies: 9
    Last Post: 06-02-2009, 08:28 AM
  3. New Building, New Units!!!
    By Fett in forum Air Conditioning
    Replies: 6
    Last Post: 19-11-2008, 03:43 PM
  4. 1 Cond Unit for 4 indoor units
    By carlfoster in forum Technical Speculations
    Replies: 7
    Last Post: 02-09-2008, 07:28 AM
  5. SR2 50 models electric SBY diagonostics made simple
    By absolute-zero in forum Transport
    Replies: 5
    Last Post: 04-01-2008, 05:11 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •