    Trane CXAH/CGAH-240 problem



    Hi

    I'm having troble reseting the ckt2 message from an Trane reversible liquid cooler, model: CXAH/CGAH-240

    I'v tried to reset the fault but it won't clear the message. The HP pressostat is tested and there is nothing wrong with any connection.

    The message that apears in the SMM module is "ckt2 fault" And reseting it with normal prosedures won't work.

    Anyone have any ideas on what this problem is?

    Thanks

    Morten



  2. #2
    Join Date
    Dec 2008
    Location
    UK
    Posts
    55
    Rep Power
    16

    Re: Trane CXAH/CGAH-240 problem

    Try Checking if the compressor overloads and Klixon`s have closed contacts. If these are open here is your problem.
    Good Luck.

  3. #3
    Join Date
    Aug 2007
    Location
    Sydney
    Age
    51
    Posts
    1,094
    Rep Power
    23

    Re: Trane CXAH/CGAH-240 problem

    Hi Morten
    If all else fails you could try a hard reset - power down (yes the big power switch) for about 20 seconds then power up again. That should clear the fault alarm if there is no fault untill it recurs, also check that any other mechanical safetys are not tripped. I had a simmilar fault on a new screw chiller this year and it was one of those mechanical safeties I thought was set but it was tripped.

  4. #4
    Join Date
    Aug 2001
    Location
    Gold Coast, Australia
    Posts
    601
    Rep Power
    28

    Re: Trane CXAH/CGAH-240 problem

    Watch out for the HP's, they're not auto resetting. There's a small (apprrox. 6mmdia.) blue dot on one side of the switch, flush with the surface. Press it in as far as you can. If it was tripped, you should hear it click as you press it.

  5. #5
    Join Date
    Apr 2009
    Location
    israel
    Age
    50
    Posts
    778
    Rep Power
    18

    Re: Trane CXAH/CGAH-240 problem

    hi the smm module hp input has to be powerd all the time for ok operation if u test the input and it is hot and u still recive the trip message try as said before power down the unit and if this fails change the module we had this happen on some of our units it is probably due to power fluctuations

  6. #6
    manikenthea's Avatar
    manikenthea Guest

    Re: Trane CXAH/CGAH-240 problem

    hi morten we had encountered same problem "ckt2 fault" in almost of our trane smm module. And what we did to rectify this problem through module software reconfiguration. We have here complete smm toolset for module repair and troubleshooting.


    fyi,

    Manny

  7. #7
    manikenthea's Avatar
    manikenthea Guest

    Re: Trane CXAH/CGAH-240 problem

    hi guys if you have defective trane smm module controller in stock/file try have it repaire on us so you could use it again without spending a new one. drop me a word on manikenthea@yahoo.com.


    manny

  8. #8
    comfortuhvac's Avatar
    comfortuhvac Guest

    Re: Trane CXAH/CGAH-240 problem

    Quote Originally Posted by MortenOlsen View Post
    Hi

    I'm having troble reseting the ckt2 message from an Trane reversible liquid cooler, model: CXAH/CGAH-240

    I'v tried to reset the fault but it won't clear the message. The HP pressostat is tested and there is nothing wrong with any connection.

    The message that apears in the SMM module is "ckt2 fault" And reseting it with normal prosedures won't work.

    Anyone have any ideas on what this problem is?

    Thanks

    Morten
    During chiller running time, put off the AHU ( Reduce the load) & once entering water temperature reduce ckt fault will be solve, then slowly increse the AHU load.

Similar Threads

  1. Problem with Trane RTAD100 chiller.
    By on4hf in forum Trouble Shooting
    Replies: 8
    Last Post: 14-10-2009, 09:01 PM
  2. Trane Techview connection problem HELP!
    By Billbo in forum Trouble Shooting
    Replies: 17
    Last Post: 26-07-2009, 11:50 AM
  3. Trane Screw Chiller ECVA 275 Compressor problem
    By pkumar68 in forum Commercial
    Replies: 3
    Last Post: 31-12-2008, 10:20 PM
  4. Trane JUAC0125B problem
    By LRAC in forum Air Conditioning
    Replies: 2
    Last Post: 28-10-2008, 09:52 PM
  5. Trane HP Defrost Board Problem
    By FastEd in forum Heat Pumps
    Replies: 8
    Last Post: 05-09-2008, 01:30 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •