    Carrier chiller 30ra/rh



    Kindly someone help me urgently, i am attending above chiller, error message was 46 which is water flow switch failure.

    1. I found there was no water circulation in the chiller. main water pipe was closed. I opened the main water tap.
    2. I purged air in all the valves.
    3. I switch on the unit, water pump was on but after few minutes alarm comes on (error message 46) & the unit shutting down.
    4. I spoke with the technician in carrier chiller, they advised me to clean the strainer. i did that so, but still error comes on.

    I checked outlet of the water flow switch, but there is a water when the pump is on.

    kindly someone help me to trouble shoot this chiller.



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Carrier chiller 30ra/rh

    Is the water flow switch responding to the water flow or has it failed?

    Switch should change over from NO to NC on water flow.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Jun 2009
    Location
    North East England
    Age
    41
    Posts
    712
    Rep Power
    19

    Re: Carrier chiller 30ra/rh

    if the floe switch is ok it could be insufficient water flow full model number please and i'll tell you the flow rate

  4. #4
    Join Date
    Oct 2010
    Location
    botswana
    Posts
    8
    Rep Power
    0

    Re: Carrier chiller 30ra/rh

    Hi Brian,

    Thank you very much for your prompt response.

    yes, water flow is responding to the water flow.

    when i tried to switch on the chiller, water pump runs 2-3 minutes. After that alarm is on then unit shutting down automatically.

    when pump is running, i checked the outlet of the valve, water was flowing.
    It seems like water flow switch is fine.

    Because water flow switch coil is warm (energising).


    Kindly give a advice how to check exactly whether water flow switch is working fine.

  5. #5
    Join Date
    Oct 2010
    Location
    botswana
    Posts
    8
    Rep Power
    0

    Re: Carrier chiller 30ra/rh

    Hi James,


    Thank you very much for your prompt response.


    Model number of the chiller is 30rab020385 sk.

  6. #6
    Join Date
    Apr 2009
    Location
    israel
    Age
    50
    Posts
    778
    Rep Power
    19

    Re: Carrier chiller 30ra/rh

    Quote Originally Posted by peterbw View Post
    Kindly someone help me urgently, i am attending above chiller, error message was 46 which is water flow switch failure.

    1. I found there was no water circulation in the chiller. main water pipe was closed. I opened the main water tap.
    2. I purged air in all the valves.
    3. I switch on the unit, water pump was on but after few minutes alarm comes on (error message 46) & the unit shutting down.
    4. I spoke with the technician in carrier chiller, they advised me to clean the strainer. i did that so, but still error comes on.

    I checked outlet of the water flow switch, but there is a water when the pump is on.

    kindly someone help me to trouble shoot this chiller.
    Hi these units might have a thermal flow switch on the outlet, with a bargraph indicating flow,these units have been known to cause trouble and need to be calibrated.
    if you have a simple differntial flow switch ,try to purge the air out of the pipes leading to the switch,
    it seems like the controller isnt getting the flow signal!
    good luck
    THE DEFINITION OF A SMART PERSON IS ONE WHOM LEARNS FROM HIS MISTAKES!!!

  7. #7
    Join Date
    Oct 2008
    Location
    mallorca, spain,
    Age
    75
    Posts
    768
    Rep Power
    19

    Re: Carrier chiller 30ra/rh

    hi if you have no water flow , and the chiller is running , its a good chance you are blowing gas not air out of the chilled water system the flow switch should stop the w-c instantly it detects no water flow.
    so first make sure you have full water flow before switching on the chiller

  8. #8
    Join Date
    Jun 2009
    Location
    North East England
    Age
    41
    Posts
    712
    Rep Power
    19

    Re: Carrier chiller 30ra/rh

    Quote Originally Posted by peterbw View Post
    Hi James,


    Thank you very much for your prompt response.


    Model number of the chiller is 30rab020385 sk.
    Single pump 1.1 l/s min
    3.5 l/s max
    Dual pump 4.4 l/s max

    what is your evap Pd

  9. #9
    Join Date
    May 2006
    Location
    scotland
    Posts
    31
    Rep Power
    0

    Re: Carrier chiller 30ra/rh

    hey peter, ive had this problem before on a carrier 30 water chiller, if its one of the really older ones, with the water flow probes in the inlet and outlet pipes, replace them, but only if you are positive that the water is pumping

  10. #10
    Join Date
    Jun 2008
    Location
    TURKMENISTAN
    Age
    44
    Posts
    14
    Rep Power
    0

    Re: Carrier chiller 30ra/rh

    alarm 46 can be another reason. first of all what kind of flow switch is this? generally carrier use electronical flow switches. u can see the response by the leds. if they r green or yellow u no alarm is comming. if red flow alarm will come. if the fs is not elec. u have follow the cable. may be there is another interlock. so often i m using evap pumps contactors NO terminals with flow switch.

Similar Threads

  1. Replies: 12
    Last Post: 27-03-2011, 04:12 AM
  2. carrier chiller 30ra/rh trouble shooting
    By peterbw in forum Technical Discussions
    Replies: 0
    Last Post: 24-10-2010, 08:15 AM
  3. Carrier chiller basic board problem
    By noushad123 in forum Trouble Shooting
    Replies: 25
    Last Post: 17-06-2010, 06:55 AM
  4. Carrier Chiller Help
    By superswill in forum Trouble Shooting
    Replies: 7
    Last Post: 18-01-2007, 10:06 PM
  5. Carrier chiller oil migration
    By lowtech in forum Industrial
    Replies: 5
    Last Post: 30-04-2006, 04:11 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •