    Question Cooling capacity and energy useage!



    Hi, can someone please explain why when the evaporating temperature is increased by 1degC the energy usage DECREASES by 3%. I understand that the cooling capacity increases by 3%, because the evaporator fills with more liquid as the txv maintains the S/H. In my ignorance the energy usage would be more as the temperatures increase and the condenser fan runs at say full speed.
    A little confused
    Thanks



  2. #2
    Join Date
    Aug 2008
    Location
    Baltics
    Age
    62
    Posts
    786
    Rep Power
    16

    Re: Cooling capacity and energy useage!

    why when the evaporating temperature is increased by 1degC the energy usage DECREASES by 3%
    Not DECREASES, but INCREASES - if by that condensing temp is kept unchanged. This means mass flow increases, therefore power consumption rises.

  3. #3
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Cooling capacity and energy useage!

    Quote Originally Posted by Burrah Boy View Post
    Hi, can someone please explain why when the evaporating temperature is increased by 1degC the energy usage DECREASES by 3%. I understand that the cooling capacity increases by 3%, because the evaporator fills with more liquid as the txv maintains the S/H. In my ignorance the energy usage would be more as the temperatures increase and the condenser fan runs at say full speed.
    A little confused
    Thanks
    You are confusing yourself with the terminology. It uses a little more energy as it runs, but shuts off a lot sooner. It is 3% more energy efficient.

    Its not the bang and its not the buck. Its the bang for the buck.

  4. #4
    Join Date
    Mar 2008
    Location
    United Kingdom
    Age
    54
    Posts
    35
    Rep Power
    0

    Re: Cooling capacity and energy useage!

    Thanks, it was just one of the questions they ask on the F-Gas practice question paper in the UK. Thanks for the help. Sometimes I wonder just WHO actually sets some of these questions as I sometimes question their answers!

  5. #5
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Cooling capacity and energy useage!

    Your COP increases
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  6. #6
    Join Date
    Aug 2007
    Location
    UK
    Age
    42
    Posts
    135
    Rep Power
    17

    Re: Cooling capacity and energy useage!

    Your energy useage decreases due to your suction pressure increasing and the compressor taking less energy to get the pressure up. The gas flow goes down so the condenser has less to do.

Similar Threads

  1. Helpful information
    By chemi-cool in forum Tools and Calculators
    Replies: 2
    Last Post: 30-10-2010, 07:00 PM
  2. Energy saving Glycol filled dry cooler circuits
    By Jasper in forum Technical Discussions
    Replies: 14
    Last Post: 19-06-2008, 02:18 PM
  3. Liquid injection vs thermosiphon oil cooling
    By Josip in forum Technical Speculations
    Replies: 25
    Last Post: 25-07-2007, 09:42 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •