Results 151 to 200 of 202
Thread: Refrigeration 101
19-10-2010, 03:16 PM #151
Re: Refrigeration 101
Gary this is great info I do appreciate it could you tell me what is meant by " if the superheat is right at( design space temp) and the subcooling is not more than 15F/8.5K then the system has the right charge.
02-11-2010, 04:26 AM #152
It is reaaly nice way you put up required basic information of refrigeration...!!! Good one...!!!
02-11-2010, 08:14 AM #153
Delta=T upper limit differs for various types of systems as well as for different design temperature and humidity requirements. And this goes beyond the scope of "Refrigeration 101".
Suffice it to say that if you are familiar with the delta-T limit for a particular type of system, anything above this limit is an unambiguous indicator of an airflow problem.
02-11-2010, 02:02 PM #154
Sir,
I am a commer to this site, well your version of refrigeration is so simple as it is communicable to every one.
Chandramouli.G
11-11-2010, 09:39 PM #155
Thanks...I follow the reasoning...it helps to grasp the basic concept(s)...you're an excellent teacher...(where would we be without IT...finding such good answers from someone on the other side of the globe, with the click of a mouse)
19-11-2010, 04:25 AM #156
29-12-2010, 12:55 PM #157
You dont sell/supply parker valves do you?
It is true, txv rarely seldom need adjusting. Only adjusted maybe 2 from STD setting after installs, all rest had to be adjusted because last bloke wound it silly for who knows why...
Is there any good threads about superheat checking/adjustment on multi evap systems? Seem to do alot of them where I'm at ATM mostly single evap/cond units previous.
I have been using evap outlet shraeder valve for evap pressures where available and pipe temp probe at bulb location for each evap coil on system - but as not all systems have evap coil access can you use sst at comp?"Old fridgies never die, they just run out of gas!"
30-12-2010, 07:07 PM #158
Gary I have been using your TECH method for years it is really great especially when you are having a bad day and can't identify a starting point.
I would encouage folk to get it and practiace it.
Steve Wright CMS
12-01-2011, 05:45 PM #159
Hi Guys,
You might be interested in the two e-books which I posted on the forum today for further reading. check them under refrigeration books.
www.isentropictemptech.com
14-01-2011, 02:34 AM #160
I am new to the HVAC field. I am an electrician by trade and have just recently complete an Associate Degree in HVACR at a local community college. I have currently started a new position in the Refrigeration Department in the chemical plant at which I work. I was recently asked to look at a Trane VAV that has no HIM on the unit. The others in the shop tell me that the Trane Techs can interface with the VAV with a laptop. I would applicate any information that may help me trouble shoot this piece of equipment. Thanks!!
19-01-2011, 06:51 PM #161
Hi Gary ,
I havn't been a member long and am currently in an apprentaship in the trade, i have about 6 months experience and things are clicking into place for a newby if that makes sense ha. I just want to say that your postings are brilliant and are helping me alot. Looking forward to reading some more many thanks
Ben
02-02-2011, 03:45 AM #162
There seems to be some confusion about saturation, so perhaps some clarification is in order:
For a given pressure, every liquid has a boiling temperature.
For example, at atmospheric pressure (0 psi) water boils at 100C/212F. We could say this is it's "boiling temperature", or since we are turning it into a vapor we could say this is it's "evaporating temperature", or since vapor bubbles are forming we could call this it's "bubble point temperature". All mean the same thing.
If we take hot steam at atmospheric pressure (0 psi) and cool it to that same 100C/212F it condenses to a liquid, so we could call this it's "condensing temperature", or since it is forming liquid droplets (dew) we could call this it's "dewpoint temperature".
All of these terms describe the same temperature point for water at 0 psi, but also describe whether we are adding or removing heat.
What if both liquid and vapor are present and we are neither adding nor removing heat? What do we call this temperature then? If we are simply describing the temperature at which the process could be driven in either direction (liquid to vapor or vapor to liquid) for water at 0 psi, we call this it's "saturation temperature".
Which terminology we use depends on whether we are simply describing the temperature point or also describing the process... so...
The saturation temperature for water at 0 psi is 100C/212F.
The evaporating temperature for water at 0 psi is 100C/212F.
The condensing temperature for water at 0 psi is 100C/212F.
02-02-2011, 04:11 AM #163
Taking this a step further, "dewpoint temperature" and "bubble point temperature" are terms we use to describe a mixture of refrigerants which have different saturation temperatures (zeotropic mixture).
Let's say we have two refrigerants.
The saturation temperature for refrigerant "A" at 0 psi is 10C/50F.
The saturation temperature for refrigerant "B" at 0 psi is 15C/59F.
If we mix these two together and are in the process of adding heat (at 0 psi), the mixture will start to bubble at 10C/50F and will finish evaporating at 15C/59F.
If we are in the process of removing heat from the mixture (at 0 psi), it will start to form dew at 15C/59F and finish condensing at 10C/50F.
The bubble point for this mixture at 0 psi is 10C/50F.
The dewpoint for this mixture at 0 psi is 15C/59F.
The difference between bubble point temperature and dewpoint temperature is called the "glide" which in this case is 5K/9F.
Note that evaporating finishes at the dewpoint temperature, so when looking at the low side pressure, we want to know the dewpoint.
Note also that condensing finishes at the bubble point temperature, so when looking at the high side pressure, we want to know the bubble point.
02-02-2011, 04:15 AM #164
And then there is pressure.
If we raise the pressure, we raise the saturation temp. If we lower the pressure, we lower the saturation temp.
The pressure/temperature (P/T) chart (aka comparator) for our refrigerant tells us the saturation temp for a given pressure. Or for zeotropic refrigerant mixtures, it tells us the bubble point and/or dewpoint.
For those who confuse zeotropes with azeotropes, here's how I remember which is which:
Just as theist means with religion and atheist means without religion, zeotrope means with glide and azeotrope means without glide.Last edited by Gary; 02-02-2011 at 04:25 AM.
02-02-2011, 05:51 AM #165
Thanks Gary - excellent.
14-02-2011, 07:47 AM #166
Re. Refrigeration 101
great information...,would you like to emphasize some thing on setting the superheat on a refrigeration system.
Fai
15-02-2011, 05:40 AM #167
Excellent explanation, thanks Gary
16-02-2011, 04:43 PM #168
- Sep 2007
- Split Croatia
- 57
- 6,175
- 6
- 36
If I recollect correctly, it is already explained as "Magoo rule" of 0,65xTD
But more detailed is here:
http://www.kueba.de/en-us/Tools/Küba...s/default.aspx
25-02-2011, 10:28 PM #169
I will concur with Gary. Keep away from the expansion valve. I've been at this a long time and have started up many supermarkets with long line ups of cases. very rarely do I have to touch a valve. Whats nice now is that some of the cases have sensors on the inlet and the outlet of the coil and supply and return air sensors. Back at the E-2 you can read superheats and splits. Makes it very convenient.
26-02-2011, 03:44 AM #170
G'Day its my 1st post to this sight , fairly new to the game , i am looking for a table of how many joules of energy each metal will absorb , i'm fairly sure there is something in arac but i can't find it , basicly table should state copper ***Kj per sq meter . Can any one help me
04-03-2011, 01:31 PM #171
Refrigerant flows very rapidly through the evaporator coil into the suction line. Many people believe that you can't have superheat until the liquid has all turned to vapor, but this is not true. Because of the velocity of the refrigerant flow it is possible to have liquid droplets surrounded by superheated vapor at the outlet of the evaporator... and in fact this is what happens. All of the liquid droplets are gone by the time there is 5-10F/3-5.5K superheat.
We want the superheat at the evaporator outlet to be low enough to ensure that we are fully utilizing the coil, thus maximizing its ability to absorb heat, but we do not want liquid droplets to be sent back to the compressor.
Similarly, it is possible to have vapor bubbles surrounded by subcooled liquid at the outlet of the condenser. All of the vapor bubbles disappear at about 10-15F/5.5-8.5K subcooling.
We want the subcooling to be high enough to ensure that we are sending sufficient liquid to the metering device, but not so high that we are backing up liquid into the condenser, thus reducing its ability to reject heat.
03-05-2011, 08:46 PM #172
Thanks for such an informative post, I am new to the field and any advice and information is greatly appreciated
17-05-2011, 06:15 AM #173
Funny you say that. I'm a sailboat owner. 5 years ago, my refigerator/freezer was not working on my boat. I pulled into a large and respectible marina and asked them if they would take a look at it. Well, they did not have time, but recommeneded that I replace the entire system from and air cooled condensor to a keel (water) cooled condensor. {hmm, a wholesale changeout on a system that is roughly 5 years old.} No, I'll pass. I ended up recharging it and made it work for another couple of seasons anyway. I now own a 30 lb can of 134a, gauges, nitrogen bottle w/ regulator, electronic leak detector and still cannot find the leak! Anyway, it's down to the bathtub pressure test.
Aside from all that good fun, the refigeration concepts have been facinating to me have lead me on a pursuit to make a better refigeration system. As I dig deeper into this topic, I find myself refering back to the Enthapy charts. It seems as though only when you know the exact pressure and temperature do you know the state of the substance.
To Gary's comment, my thought is that even though it is technically feasible to design a system that would diagnose itself, I doubt the Product Management or Marketing Department would allow it due to expense. That is my OPINION. Would you agree? I think we could have the ideal system if we could monitor and control the proper parameters. It is possible, and I just might do it with some help.
20-05-2011, 11:59 PM #174
30-05-2011, 05:33 PM #175
hey,
im pretty new this forum, and i dont know how to create my own thread. anyway...im a student in my final year of my degree in construction project management, and i am doing a dissertation on air conditioning, but i dont know what to talk about. the title will most probs be "Air conditioning and Environmental issues" but i seriously dont know what to talk about, so i would appreciate if you guys could give me some advice, and point me the right direction?
thank you
Naeem
08-07-2011, 10:47 AM #176
Dear Gary,
I have been encountered with aproblem of Oil nonreturning back to the compressor in an R22 system connected to an flake ice plant evaporating at -20C.The flaker is fed through 7nos TXVs and a hand regulating valve.I recon itis an TxV problem and what sort of superheats should yu allow. At the moment ir is set at 7 C.
patrickj
24-07-2011, 02:13 PM #177
On AC systems its the outlet side of the condenser, on refrigeration units its usually at the drip since I ususally can't get onto the outlet of the condenser. Wouldn't the liquid line just outside the reciever be the larger/greater subcooling difference?
BTW, someone stoll my books, where can I get replacements?
Rich
24-07-2011, 05:38 PM #178
25-07-2011, 12:54 PM #179
Subcooling should be measured on the liquid line after the receiver. Keep in mind that the liquid line cannot be cooler than the air surrounding it. If the liquid line is in the hot air stream leaving the condenser, it will measure abnormally high.
Move down the liquid line until it enters an area that is surrounded by ambient air. That's where you measure the subcooling.
18-08-2011, 10:27 PM #180
First of all thank you Gary and all of you for sharing your knowledge.
Second of all, picture this:
- a sistem used in air conditioning: 5 C evap, 40 C cond, txv with no MOP, runing, in normal conditions with SH = 5k and SC = 4K, about 30 kw compressor capacity (it's a purely ipotetic system), R407c
- according with txv producer (let's say Danfoss - TEZ 5 with orifice no.2), the valve has a capacity of 30 kw at a TXV DP of about 12bar; the capacity rises with the TXV DP rise
- with a high load, the superheat rises, the txv opens and the TXV DP decreases thus it's capacity decreases, so the sistem capacity decreses too, leading to a increasing suply air temperature.
What is wrong ?
19-08-2011, 02:59 PM #181
I think you are confusing TXV capacity ratings with system output.
Let's say an elevator has a capacity rating of 10 people. Does that mean there are 10 people on the elevator? Nope.Last edited by Gary; 19-08-2011 at 03:02 PM.
23-08-2011, 03:37 PM #182
I'm well aware that the things are not going that way. The txv will open to increase the system capacity, to reduce the superheat and the thv dp will decrease. Then what is the table i've attached from Danfoss doc. saying ?
23-08-2011, 04:06 PM #183
The table is telling you the maximum flow (valve wide open) for a given dP... and you are still confusing capacity with output. Opening the TXV does not increase the capacity of the system, it increases the flow and thus the output.
23-08-2011, 04:19 PM #184
Question Sir <Gary>
Liquid line (on water chiller) should be subcooled liquid coming from condensor
Sun beating down on tube-work
I am expecting now saturated liquid (lots of flash gas)
Could you explain for me please (technically or simply put)
What is in this liquid line now ?
R's chillermanIf the World did not Suck, We would all fall off !
23-08-2011, 04:52 PM #185
23-08-2011, 05:04 PM #186
23-08-2011, 06:08 PM #187
Given the curvature of the liquid line, along with the reflective properties of the metal and the relatively small size, I suspect the solar heat gain would be negligible. I would certainly not expect lots of flashing.
23-08-2011, 07:20 PM #188
06-09-2011, 01:49 AM #189
A basic question, Gary.
Given a system running in Cooling mode, how to raise evaporating temp (or pressure)? Different ways to do so?
My condensing ~50C but evaporating ~ -3, quite low for an A/C.
Try to open the TXV apperture until getting low limit SH but failed to raise Tevap muchly.
Anything to do with indoor air flow rate? I was trying to maintain a 10% lower air flow rate than initial calculation for noise benefit.
06-09-2011, 04:45 AM #190
Given a fully active evap coil, the pressure/temperature will depend upon the amount of heat being transferred from the air to the refrigerant. The more heat transfer, the higher the pressure/temperature.... and vice versa. The rate of heat transfer depends upon the surface area, the volume of air flowing through the coil and the temperature of the air flowing through the coil.
It is a mistake to believe that a pressure/temperature is, in and of itself, too high or too low. In truth, the temperature/pressure may or may not be too high/too low for a particular design under a given set of conditions.
In this case, the evap being the outdoor coil, on a cool day -3C is probably not low at all. It depends.Last edited by Gary; 06-09-2011 at 04:54 AM.
06-09-2011, 05:05 AM #191
06-09-2011, 06:10 AM #192
Thanks for your insights, at least I know that my thought was not far off to explain the situation.
Agree with you, airflow is so important and I hate forcing myself reducing it. But have to factor in noise level, can't make it quiet, cant sell.
I considered Tevap low compared to initial calculated system balance. Such a low evap temp will affect system efficiency as well. Small compressor is now designed for high efficiency and is most efficient at approx Tevap ~ 5C or more. Stucked with airflow and coil size so could not improve it. And if you read my other post, it affects heating mode as well (high head pressure). Too much compromises just for noise.
08-09-2011, 12:49 AM #193
Off topic - needed removing
18-10-2011, 02:26 PM #194
Gary, what do you think about using compressor superheat to analyse system performance? Checking discharge line temps and subtracting saturated liquid pressure. Something like 50 to 70 degrees as normal range.
18-10-2011, 11:29 PM #195
Discharge superheat is directly related to compressor inlet superheat. The higher the inlet superheat, the higher the discharge superheat... and vice versa. I use inlet superheat and it tells me what I need to know. I don't know much about discharge superheat, because it is not something I use.
25-10-2011, 11:04 PM #196
Sorry to but in. I work on chillers for industrial. Supplying cooled water for various machines. A sub cooling of 15oc should be acheavable with any system there or about and 5oc superheat give or take. If you are not acheiving this its the same route. Gas charge/condensor fault/evap fault/ tev fault/ and abnormal ambient range. Your gauges are your friend and a simple logical reason. Look for signs like liquid return to compressor(bottom iced up) or tev iced up, mass dt across evaporater, low diff across condenser etc
25-10-2011, 11:10 PM #197
Oh and possibly water blockage on water side or pump failure all water / process side. Anything slowing down heat exchange
25-10-2011, 11:11 PM #198
In that case check pump curves - completely different game but very easy to grasp.
25-10-2011, 11:17 PM #199
Spoon Man
a condensor has 3 jobs to do when rejecting heat
de-superheating (specific heat rejection)
condensing (latent heat rejection)
subcooling (specific heat rejection)
the last subcooling depends if the coil has been sized accordingly to subcool the refrigerant and to what degree, industrial refrigeration will subcool the already de-superheated/condensed refrigerant but most package chillers dont subcool to 15*c, in fact many struggle to reach 6*c
Exactly what make/model are you referring to ??? @ 15*c many will be overcharged
30-10-2011, 10:32 PM #200
Subcooling at 15K is way too high, causing liquid to back up into the condenser, reducing it's effective area and therefore it's efficiency. I would recommend max 8.5K/15F subcooling or clear sightglass, whichever comes first.
advanced refrigeration technology
By Lc_shi in forum FundamentalsReplies: 10Last Post: 16-02-2011, 06:22 PM