    Re: Refrigeration 101

    Refrigeration System

    1/Refrigeration system overview
    *Propane Chiller: 57% Level
    *LPG OH Condenser: 80% Level, LPG T°: -36°C
    *Propane Economizer: 40% Level, PCV: 6 Bar, T° Gas: 9.5°C
    *02Propane Compressor:
    -PRO “A” -PRO”B”
    .Capacity Control:
    Set point (Bar) O.5 0.5
    PID Out: 100% 100%
    .High Stage Capacity Control:
    Set point: 3.5 3.5 Bar
    PID Out: 100% 100%
    .Moy Amperes (Amp) 60.2 58.5
    .Suction Pressure (Bar): 0.82 O.91
    .Suction Temp (°C) : -41.3 -41.2
    .Suction SH (°C): 5.0 3.3
    .Intermediate Pressure (Bar): 4.0 4.4
    .Intermediate Temp (°C) : 50.8 49.2
    .Intermediate SH (°C): 55.5 51.6
    .Discharge Pressure (BAR) : 13.5 13.8
    .Discharge Temp (°C) : 74.0 72.1
    .Discharge SH (°C) : 34.7 31.8
    →Bypass Propane Condenser used in manual 0%
    *Propane surge drum:
    .Pressure: 14.5 Bar
    .Level: 52%
    *Gas Propane Exchanger:
    .Propane T°: 34.75°C
    .Gas T°: 29.25 °C
    2/ Refrigeration Skid:
    *Inlet Cold Separator: 26.4c°C
    *Outlet Cold Separator: -28 °C
    *Level Cold Separator: 40%
    *Set point TCV: -45 °C (Bypass Cold Separator)
    *Gas / Liquid Exchanger :
    . Gas T°: 36.75 °C
    .LPG T° : 8.85 °C
    *Gas / Gas Cooler :
    .Gas T° to sweet / sales gas Exchanger : 4 °c
    .Gas T° to propane chiller: -16 °C
    →*we can’t attend the cold Temperature -45°C
    *Same times we have carryover of liquid on Propane Receiver
    Please help me to identify the problem and correct them.