    Re: Refrigeration 101

    Quote Originally Posted by chillyblue View Post
    How high is high, 8, 10 ,20, 30, 50???????????
    and if it is high what indication can you get from the evap that it is performing correctly,
    Your indication comes from the condenser. Given a normal load, and assuming good condenser airflow, the SCT should be 20-35F/11-19K above the ambient (condenser air in) temperature (20-35F/11-19K cond TD), depending upon the relative coil sizing. If the heat load being rejected by the condenser is normal, then the heat load being absorbed by the evaporator must also be normal.
    Last edited by Gary; 28-07-2009 at 08:32 PM.

  2. #2
    Join Date
    May 2007
    Location
    Northants
    Posts
    290
    Rep Power
    17

    Re: Refrigeration 101

    Quote Originally Posted by Gary View Post
    Your indication comes from the condenser. Given a normal load, and assuming good condenser airflow, the SCT should be 20-35F/11-19K above the ambient (condenser air in) temperature, depending upon the relative coil sizing. If the heat load being rejected by the condenser is normal, then the heat load being absorbed by the evaporator must also be normal.
    Thanks Gary, thats great help thanks.
    could you confirm what happens if you have a high load and a low load??
    I'm assuming with a high load the SCT will reduce below 11-19K above air on to condenser and with a low load the SCT will increase to more than 11-19k above air on to cond.
    I'm also assuming that under high conditons your subcooling will be less and with low load conditions your subcooling will more

  3. #3
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Refrigeration 101

    Quote Originally Posted by chillyblue View Post
    Thanks Gary, thats great help thanks.
    could you confirm what happens if you have a high load and a low load??
    I'm assuming with a high load the SCT will reduce below 11-19K above air on to condenser and with a low load the SCT will increase to more than 11-19k above air on to cond.
    Just the opposite. High load increases SCT and low load decreases SCT... and SCT above ambient (cond TD) should remain within the 11-19K range.

  4. #4
    Join Date
    May 2007
    Location
    Northants
    Posts
    290
    Rep Power
    17

    Re: Refrigeration 101

    Quote Originally Posted by Gary View Post
    Just the opposite. High load increases SCT and low load decreases SCT... and SCT above ambient (cond TD) should remain within the 11-19K range.
    If the ambient air onto the condenser remains the same and the sct decreases with low load then the cond td must get bigger.
    If the ambient air onto the condenser remains the same and the sct increases with high load then the cond td must get smaller.

    do you mean that with a high load the cond td would be around 11k (smaller) and low load would be around 19k (larger)

    CB

  5. #5
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Refrigeration 101

    Quote Originally Posted by chillyblue View Post
    If the ambient air onto the condenser remains the same and the sct decreases with low load then the cond td must get bigger.
    If the ambient air onto the condenser remains the same and the sct increases with high load then the cond td must get smaller.

    do you mean that with a high load the cond td would be around 11k (smaller) and low load would be around 19k (larger)

    CB
    No... No... and No.

    Let's say the ambient is 25C and the SCT is 36C. The TD is 36-25=11K.

    The SCT then rises to 40C. The TD is 40-25=15K .

  6. #6
    daviddwilson's Avatar
    daviddwilson Guest

    Re: Refrigeration 101

    Quote Originally Posted by Gary View Post
    Just the opposite. High load increases SCT and low load decreases SCT... and SCT above ambient (cond TD) should remain within the 11-19K range.
    There will be relatively little change in subcooling as the liquid line temp will tend to rise and fall with the SCT and a TXV system stores sufficient surplus liquid refrigerant to compensate for variations in load without substantial changes in subcooling.

  7. #7
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Refrigeration 101

    Quote Originally Posted by chillyblue View Post
    I'm also assuming that under high conditons your subcooling will be less and with low load conditions your subcooling will more
    There will be relatively little change in subcooling as the liquid line temp will tend to rise and fall with the SCT and a TXV system stores sufficient surplus liquid refrigerant to compensate for variations in load without substantial changes in subcooling.