Results 1 to 50 of 202
Thread: Refrigeration 101
24-05-2010, 06:57 AM #1
Re: Refrigeration 101
Gary,
When you say "Generally speaking, a freezer should have 6-8F/3.5-4.5K superheat, a cooler should have 8-10F/4.5-5.5K superheat, and an A/C should have 12-16F/6.5-9K superheat."
At what abient temp are we talking here?
75 degree's?
25-05-2010, 06:05 AM #2
28-05-2010, 06:56 AM #3
In my heat-pump trials, I have observed an influence on evaporator SH, due to ambient air temperature movements.
If Ta,in falls during the range of test, SH will roll down a little more than if Ta,in is constant.
If Ta,in rises during the range of test, SH can often end up being almost constant over the test duration.
The influence can be in the range of ~ 1-3K, depending on the operating SH of the machine.Engineering Specialist - Cuprobraze, Nocolok, CD Technology
28-05-2010, 08:07 AM #4
28-05-2010, 08:22 AM #5
28-05-2010, 08:31 AM #6
advanced refrigeration technology
By Lc_shi in forum FundamentalsReplies: 10Last Post: 16-02-2011, 05:22 PM