    Oil return problems

    Freezer store-room, installed 1994.
    Original situation: 2 independent Copeland Demand-cooling compressor (R22) on 2 KUBA evaporators, electrical defrost. Danfoss TE5.
    No oil separator nor suction accumulator.
    2 HE’s in the discharge for make-up water for the ground heating.
    Since the install no big problems. (broken heater in the evaporator, condenser fan fault,…)

    Round March this year, one compressor went in fault. Piston was broken.
    Reason??
    Client does minor repairs themselves and sometimes when a heater in the evaporator is broken, they wait to repair it till they have 2 or more broken heaters or unit is completely frosted.
    Possible cause: ***** washout in the sump??

    Installed a new compressor, standard compressor (no demandcooling) and retrofitted to R404a. Blow out the lines (+/- 80 to 100 ft) with OFN. Let it run on POE and replaced after 4 hours running with new POE.
    After 1 day, replaced oil again.

    Appr. 10 days later, call from clientà New compressor went in fault.
    Cause: broken pistons.
    No oil in sump.
    Searched for fault: tech had installed a new TE5 and installed an orifice 3 instead of a 1.
    ***** washout.

    Installed new compressor. SH within the limits (20 K measured at inlet compressor)
    After 1,5 months running, again strange noise (knocking metal noise) in compressor. It’s just like a piston is has too much spacing. Again, almost all the oil has gone out of the sump.
    Checking Oil Safety device: wired wrong by ‘someone’

    Is oil return so worse with R404a compared with R22?
    Speed in the suction lines is approximately the same.
    We did retrofits in supermarkets with more then 2000 ft of lines and never had those problems.
    Also never had oil return problems with R22, at least no such a problems.

    Installing an (coalescent?) oil separator?
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  2. #2
    Join Date
    Jan 2002
    Location
    Long Beach Ca
    Age
    48
    Posts
    47
    Rep Power
    0

    Re: Oil return problems

    mornin Peter! i would check evapps clear , clean, sh, install standard oil separator, sounds like key is unclear(icing) coils ecessive run times low sh and velocity, parralel compressors or independent compressors? if parr. which stage problem?

  3. #3
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: Oil return problems

    Hi Peter.

    In all the oil problems I had, always after changing the orifice to a smaller one and installing oil separator, problems has gone.

    One more thing you can do is making a 1/4 pipe with SV from the lower point at the collector pipe at the evaporator to the suction line operating via a timer controlled by the compressor main contactor.

    I have done this on a unit where the evaporator wes 20m below the condensing unit. No oil problems there anymore.

    Chemi

  4. #4
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Oil return problems

    Thanks already, just a quick reply while eating


    2 independent compressors and evaporator is +/- 4 m above the compressor, lines sloped towards compressor.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  5. #5
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: Oil return problems

    Bon appetite Peter.

    Still, check the evaporator design and see how the pipes are arranged.
    The oil is there somewhere.

    Chemi

  6. #6
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Oil return problems

    That's true and it only can be in the pipes or evaporator.
    But why weren't there any problems during almost 10 years with R22? That's bothering me now.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

Similar Threads

  1. R-508B oil return problems
    By Hank Hill in forum Industrial
    Replies: 43
    Last Post: 05-02-2010, 05:58 PM
  2. Problems LG don't want you to know about
    By Andy W in forum Air Conditioning
    Replies: 11
    Last Post: 16-02-2006, 04:52 PM
  3. oil pressure problems on air dryer
    By edge in forum Trouble Shooting
    Replies: 1
    Last Post: 16-07-2002, 02:10 PM
  4. return air
    By subzero*psia in forum Air Conditioning
    Replies: 1
    Last Post: 12-07-2001, 04:02 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •