    R404a Oil Return



    To expand on a section of the oil return problem thread.

    Could it be argued that it would benefit the system if R290 was added as standard to all R404a systems to aid oil return.

    My main querys are would this eliminate the need for oil separators and simplify the system and what 290 to 404a ratio should be used (does everyone just add a little and see how it goes?) keeping in mind the regs for HC gases.



  2. #2
    Join Date
    Jan 2004
    Location
    Southern California
    Posts
    7
    Rep Power
    0

    Re: R404a Oil Return

    Please explain why you need to add R-290 to bring back oil. I have designed many R-404A system and retrofitted HCFC 502 systems to R-404A with suction temps to -40F and I have never had the requirement to add a HC solvent to bring the POE back. With the right suction gas velocities and line slope it should'nt be problem

Similar Threads

  1. R507 instead R404a?
    By Friobernal in forum Refrigerants
    Replies: 49
    Last Post: 09-04-2011, 12:42 AM
  2. pressure drop of pump return line ammonia
    By Moeller in forum Fundamentals
    Replies: 5
    Last Post: 04-09-2007, 05:21 AM
  3. Refrigeration Cases and Return Air
    By Capt Steve in forum Supermarket Refrigeration
    Replies: 2
    Last Post: 10-02-2005, 07:02 AM
  4. Oil return problems
    By Peter_1 in forum Industrial
    Replies: 37
    Last Post: 23-08-2004, 11:30 PM
  5. return air
    By subzero*psia in forum Air Conditioning
    Replies: 1
    Last Post: 12-07-2001, 04:02 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •