    Relay sparks!!!! cooler not going cold!!!



    Hello

    I have a 4 door dumper fridge it is not cooling.

    It is a commercial fridge stainless steel Not that that matters much.

    Anyway the complaint is it is not cooling, There is some ice build up on the back of the evaporator.

    I have checked the pressures and they seem to be correct.

    The compressor is very very hot and also is the condenser (75 degrees C).

    So i have checked the relay.. It clicks and there is a blue spark when it starts.

    The compressor starts as well. However within a second there is a second spark inside the relay....

    I am thinking that the relay is faulty and will need changing

    any thoughts please let me know... Relay or capasitor?

    But the Compressor is working BUT HOT



  2. #2
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Relay sparks!!!! cooler not going cold!!!

    Evap air in temp
    Evap air out temp
    Low side pressure/saturated suction temp
    Suction line temp at TXV bulb

    Cond air in temp
    Cond air out temp
    High side pressure/saturated condensing temp
    Liquid line temp at receiver/condenser outlet

  3. #3
    Join Date
    Jun 2009
    Location
    spain
    Age
    46
    Posts
    15
    Rep Power
    0

    Re: Relay sparks!!!! cooler not going cold!!!

    All I can say is that the evap temp in general is 8 degrees C...

    The con temp is 75 Degrees C.

    On this fridge I can only check pressures via a service valve on the top of the comp...

    Dont have valves on high side and the low side.

    Not a very big comp

  4. #4
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Relay sparks!!!! cooler not going cold!!!

    We need as many of these temps/pressures as you can get.

  5. #5
    Join Date
    Aug 2008
    Location
    Baltics
    Age
    62
    Posts
    786
    Rep Power
    16

    Re: Relay sparks!!!! cooler not going cold!!!

    If relay that "sparks", it is evidently not good already.
    The burning relay, however, may be only a consequence of another fault.
    Maybe RUn capacitor bad (if such there is), or the compressor is "braking" during runtime, both making the start relay constantly switching on and off the START capacitor.
    Fridge is most probably heavily overloaded.

  6. #6
    Join Date
    Dec 2007
    Location
    lebanon
    Posts
    130
    Rep Power
    17

    Re: Relay sparks!!!! cooler not going cold!!!

    hi
    size of compressor and ***** is it original
    were did u measure 75degree if after the drier u must check if the condenser is clean if so air in &air out.
    check compresser amp if its high it makes relay energises stsrt windings that what making relay sparks &comp hot

  7. #7
    Join Date
    Jun 2009
    Location
    spain
    Age
    46
    Posts
    15
    Rep Power
    0

    Re: Relay sparks!!!! cooler not going cold!!!

    Will have to check these out.

    I will have to check the relay and cap....

    The temp I have taken is on the condenser its self.

    What I did notice was when I put the gage on the only service valve which is on the top of the comp some oil smelling stuff came out..

    Could this be moisture etc......

  8. #8
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Relay sparks!!!! cooler not going cold!!!

    Quote Originally Posted by coolrunnings1 View Post
    What I did notice was when I put the gage on the only service valve which is on the top of the comp some oil smelling stuff came out..
    Could this be moisture etc......
    I think the oil from the cap entered the refrigeration circuit via the leads and came this way into the circuit and contaminated the refrigerant.
    This contamination now blocks the starting relay.
    Last edited by Peter_1; 06-07-2009 at 12:33 PM.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  9. #9
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: Relay sparks!!!! cooler not going cold!!!

    Quote Originally Posted by Peter_1 View Post
    I think the oil from the cap entered the refrigeration circuit and came this way into the circuit and contaminated the refrigerant.
    This contamination now blocks the starting relay

    I hate it when this happens Much better with three phase stuff imho.
    Last edited by Peter_1; 08-07-2009 at 07:31 AM.

  10. #10
    Join Date
    Jun 2009
    Location
    spain
    Age
    46
    Posts
    15
    Rep Power
    0

    Re: Relay sparks!!!! cooler not going cold!!!

    So if I replace the cap would this help also changing the relay.

    ???????

  11. #11
    Join Date
    Jun 2009
    Location
    spain
    Age
    46
    Posts
    15
    Rep Power
    0

    Re: Relay sparks!!!! cooler not going cold!!!

    Quote Originally Posted by coolrunnings1 View Post
    So if I replace the cap would this help also changing the relay.

    ???????
    Comp would only be a 1 phase also

  12. #12
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: Relay sparks!!!! cooler not going cold!!!

    I'd want to have an amp probe/current meter on the live feed to the compressor to see how much current it is pulling, sparking could be klixon operating if compressor is pulling too much power. And to test capacitor with a meter also.

    Could be faulty relay/capacitor stopping compressor from running properly or faulty compressor (partly siezed, or shunted windings) making relay chatter. Or a blockage making the compressor run with too high a discharge pressure.

  13. #13
    Join Date
    Jun 2009
    Location
    spain
    Age
    46
    Posts
    15
    Rep Power
    0

    Re: Relay sparks!!!! cooler not going cold!!!

    Quote Originally Posted by monkey spanners View Post
    I'd want to have an amp probe/current meter on the live feed to the compressor to see how much current it is pulling, sparking could be klixon operating if compressor is pulling too much power. And to test capacitor with a meter also.

    Could be faulty relay/capacitor stopping compressor from running properly or faulty compressor (partly siezed, or shunted windings) making relay chatter. Or a blockage making the compressor run with too high a discharge pressure.

    That was next thing to try. However was going to do the job today and just found out that my bro got house broke into this morn DOH!!! Crime here in Tenerife is on the rise.

    Anyway will try these prob tomorrow now any other thoughts are welcome

  14. #14
    Join Date
    Feb 2008
    Location
    adelaide sth.oz
    Posts
    1,015
    Rep Power
    19

    Re: Relay sparks!!!! cooler not going cold!!!

    all relays were black in the old days hence no arcing was ever seen
    mmm to beer or not to beer...........lets drink breakfast

Similar Threads

  1. Cannot get the cooler to temp
    By coolrunnings1 in forum Fundamentals
    Replies: 13
    Last Post: 27-06-2009, 07:51 PM
  2. Air cooler broken
    By Rio69 in forum Trouble Shooting
    Replies: 5
    Last Post: 26-06-2009, 02:47 PM
  3. cold river water
    By eftimios in forum Fundamentals
    Replies: 8
    Last Post: 09-11-2008, 06:37 PM
  4. Hermetic analyzer " ANNIE" how do they work
    By kengineering in forum Tools and Calculators
    Replies: 11
    Last Post: 02-03-2008, 06:10 PM
  5. voltage drop on relay
    By Temprite in forum Electrical
    Replies: 4
    Last Post: 30-01-2006, 07:55 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •