    hi all, im not an engineer, just interested in learning, practice and theory, but have a question thats been niggling me!

    my mum has a daikin inverter system, because the indoor unit has an electronic tev would the suction pressure stay the same regardless ?

    and even if not what would the pressures be?

    can ne 1 explain??

    many thanks ian



  2. #2
    Join Date
    May 2008
    Location
    cheshire uk
    Age
    45
    Posts
    34
    Rep Power
    0

    Re: daikin suction pressure!

    forgot to say its 1 r410a system

  3. #3
    Join Date
    Aug 2008
    Location
    Baltics
    Age
    62
    Posts
    786
    Rep Power
    16

    Re: daikin suction pressure!

    I would say at 25C ambient the suction pressure will be kept about 10 bar and at 18C about 7.5 bar.

  4. #4
    Join Date
    May 2008
    Location
    cheshire uk
    Age
    45
    Posts
    34
    Rep Power
    0

    Re: daikin suction pressure!

    well i got that totally wrong...

    assumed the return tempwouldnt vary ie txv controlling it, because the temp is known the pressure would be as well?

    pls help me get my head around this lol
    v confused, ian S

  5. #5
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: daikin suction pressure!

    The pressures vary according to the temperature and volume of the air flowing through the coils.

  6. #6
    Join Date
    Aug 2008
    Location
    Baltics
    Age
    62
    Posts
    786
    Rep Power
    16

    Re: daikin suction pressure!

    While the return air temp is not changing, the quantity of the boiling refrigerant in the evaporator will not be changing (so, pressure).

    Becomes return air temp lower, the metering system let less refrigerant into the evap (both leading to suction pressure falling); becomes higher, let more (pressure rising).

  7. #7
    Join Date
    May 2008
    Location
    cheshire uk
    Age
    45
    Posts
    34
    Rep Power
    0

    Re: daikin suction pressure!

    right.. im totally head mashed!

    1st of all im not so good at getting over things that i mean.. lol

    i was actually going on about the line (pipe) temperature

    and 2nd the way i was lead to believe the system works (its an inverter)
    is that the compresser monitors high pressure side and varys the speed of it to keep the pressure constant (ie more demand = more speed at compressor needed.

    some 1 told me that because the system is an inverter with an electronic tev that the suction pressure should remain constant..
    (is this bulls*#t ??)

    his explanation being that cos the tev monitors evap coil exit temp and keeps that constant?!? that the temp will be known to!!!!!

    i am not sure, but i tend to think not!
    can any 1 help?

    he is a refrigeration engineer, but to be honest i cant get this into my head!!!

    begging to think im gleaming snippits of info off the worng person!!

    cheers guys

    ian

  8. #8
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: daikin suction pressure!

    Quote Originally Posted by totalacedude View Post

    and 2nd the way i was lead to believe the system works (its an inverter)
    is that the compresser monitors high pressure side and varys the speed of it to keep the pressure constant (ie more demand = more speed at compressor needed.
    Wrong! Compressor is governed by complex algorithm.

    some 1 told me that because the system is an inverter with an electronic tev that the suction pressure should remain constant..
    (is this bulls*#t ??)
    Yes!
    his explanation being that cos the tev monitors evap coil exit temp and keeps that constant?!? that the temp will be known to!!!!!
    Wrong! Electronic TEV keeps evaporator superheat (not temperature/pressure) as complex algorithm requires.


    he is a refrigeration engineer, but to be honest i cant get this into my head!!!

    begging to think im gleaming snippits of info off the worng person!!
    If your interpretation of his words are correct then you "gleaming snippits of info off the worng person".

  9. #9
    Join Date
    Aug 2008
    Location
    Baltics
    Age
    62
    Posts
    786
    Rep Power
    16

    Re: daikin suction pressure!

    Difference inverter/non-inverter - the former more energy efficient.

    Non-inveter copmpressor pump around refigerant with almost the same power consumed at 30C room temp and at 20C room temp - let's say, 5A and 3,5A respectively.

    Inveter compressor's power consumed will be reduced to, let's say, 1.5A at 20C room temp (from the 5A at 30C).

    I believe suction pressures still differ at 30C and at 20C on inverter.

  10. #10
    Join Date
    May 2008
    Location
    cheshire uk
    Age
    45
    Posts
    34
    Rep Power
    0

    Re: daikin suction pressure!

    well im glad i came here ans started asking questions!!!

    any good sources of info flying around net any where??? for me to peruse and learn CORRECTLY!!!

    CHEERS IAN

Similar Threads

  1. Superheat and Subcooling
    By Chunk in forum Fundamentals
    Replies: 42
    Last Post: 15-01-2011, 01:24 AM
  2. Suction Discharge Pressure Equalises After Cut Off
    By pramodphilip in forum Trouble Shooting
    Replies: 9
    Last Post: 23-06-2008, 07:38 PM
  3. Suction pressure problem during defrost
    By Etienne in forum Fundamentals
    Replies: 6
    Last Post: 05-01-2007, 06:48 AM
  4. Interesting Problem
    By NH3LVR in forum Industrial Compressors
    Replies: 13
    Last Post: 12-08-2006, 10:27 PM
  5. Building a wine cabinet
    By Rory in forum Technical Discussions
    Replies: 38
    Last Post: 13-07-2004, 08:28 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •