    Need answers on a freezer....



    I've got a refrigeration system on one of my rental trailers that is having some issues that I've never come across before in my 16 years of working on this stuff. Let me give you a list of the components and a run down of what I've done to try and repair the problem.

    The box is 6'x8'. It has Copeland condensing unit model# EJAL-A100. The compressor is a Copeland model # KAEB-007E-CAA. The evaporator is a 5400 btu with a BFSE-AA-ZP TXV. System runs on 404a refrigerant.

    The problem I'm having is that the box won't pull cooler than 40-45 degrees. I did a compressor efficiency test and it would only pull to 2 inches in a vac, so i put a set of valves in it. That changed nothing. So I checked the TXV and it didnt seem to be feeding the coil. It also took a long time for the fans to come on because of that. So I opened the valve a round and nothing changed again. So I put a new valve and nothing again. The system is running 35 lbs of suction and 320 lbs of head pressure. I checked for pressure drops in the system and I'm only getting 2 degrees TD across the evap coil. This thing also has a new condensor on it because the old one had a leak a couple of yrs ago. This thing was running great until afew weeks ago. Hopefully I made some kind of since in describing my problem. thanks in advance for the help.....

    Todd



  2. #2
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Need answers on a freezer....

    What's the subcooling and superheat?

  3. #3
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Need answers on a freezer....

    That 2F TD I assume is the air in minus air out temps. That is the delta-T or dT, not the TD. The TD is air in minus saturated suction temp (SCT), which in your case is about 40F TD.

    The dT is way too low and the TD way too high. I'm betting that the superheat is also way too high... all of which tells me that the coil is starving.

    Since this is a new TXV, either the system is undercharged or there is a restriction between the condenser and the TXV. Plugged drier... or kinked liquid line? Wherever the restriction is there should be a temp drop across it.

  4. #4
    Join Date
    May 2006
    Location
    USA
    Age
    50
    Posts
    14
    Rep Power
    0

    Re: Need answers on a freezer....

    I do have a clear sight glass and I have checked for a pressure drop from the reciever tank to the TXV thru a tap that I welded in 2" before the TXV. The coil is starved no doubt. I can get the first set of loops to frost and it takes quite awhile for the fan delay to come in. I don't know the superheat at this point because I have the TXV wide open and cant get it to feed all of the coil.

  5. #5
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Need answers on a freezer....

    Quote Originally Posted by ToddH View Post
    I do have a clear sight glass and I have checked for a pressure drop from the reciever tank to the TXV thru a tap that I welded in 2" before the TXV.
    Then that narrows it down to that last two inches... or the TXV itself. Does the TXV feed into a distributor? If it does, then add that to the list.

  6. #6
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Need answers on a freezer....

    You might want to disconnect the TXV and blow backwards through the coil to see if it flushes anything out of there.

  7. #7
    Join Date
    May 2006
    Location
    USA
    Age
    50
    Posts
    14
    Rep Power
    0

    Re: Need answers on a freezer....

    I've flushed everything 9 ways to sunday. And yes it goes into 3 distributor tubes. And I just added the tap at the TXV to check the pressure drop from the reciever tank so I know the last 2" is clear.

  8. #8
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Need answers on a freezer....

    Quote Originally Posted by ToddH View Post
    The evaporator is a 5400 btu with a BFSE-AA-ZP TXV.
    Hmmmm... the ZP charge in the TXV bulb is a pressure limiting charge. This chokes off the flow to prevent the suction pressure from going too high and overloading the compressor.

    We need to check the high side stats to see if it is pumping a full load:

    Condenser air in/air out temps
    High side pressure
    Liquid line temp near receiver

  9. #9
    Join Date
    May 2006
    Location
    USA
    Age
    50
    Posts
    14
    Rep Power
    0

    Re: Need answers on a freezer....

    This particular piece of equipment is on a small insulated trailer in our rental fleet so every time this thing goes out it starts working with a high box temperature. Lately it's been starting with a 85-90 degree f box temp during our "repairs". (haha). I do know that the head has been running around 310-325 lbs with a full sight glass. I was hoping once I cleared it it would bring it back down under 300. As the box gets cooler the head might get to 300 even. The air inlet and outlet temps I don't remember off hand ( I didnt do the test) but I do recall only a 6 degree differential. I haven't checked the liquid line temp but I can tell by the good old hand test it seems way too hot to me. I took the discharge line off yesterday to look for a possible restriction but nothing was found. also keep in mind this is a relatively new condenser that is very clean. Thanks for the help so far Gary.

  10. #10
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Need answers on a freezer....

    I can't see it from here. The only way I can "see" what the system is doing is if you give me accurate temperature and pressure measurements.

  11. #11
    Join Date
    Feb 2008
    Location
    adelaide sth.oz
    Posts
    1,015
    Rep Power
    19

    Re: Need answers on a freezer....

    apply water over condenser to see if pressures improve,maybe condenser is to small or its configuration of piping maybe incorrect.
    mmm to beer or not to beer...........lets drink breakfast

  12. #12
    Join Date
    May 2006
    Location
    USA
    Age
    50
    Posts
    14
    Rep Power
    0

    Re: Need answers on a freezer....

    Lowcool- I sprayed water on the condensor and got 250 lbs of head for 45 minutes and only pulled 5 degrees out of the box.

    Gary- What are all of the reading you need? when I get in monday morning I'll get these and report back in the evening. Thanks again.

  13. #13
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Need answers on a freezer....

    Evap air in temp
    Evap air out temp
    Low side pressure
    Suction line temp at TXV bulb

    Cond air in temp
    Cond air out temp
    High side pressure
    Liquid line temp at receiver outlet

  14. #14
    Join Date
    May 2006
    Location
    USA
    Age
    50
    Posts
    14
    Rep Power
    0

    Re: Need answers on a freezer....

    I'll get those and post tomorrow...

  15. #15
    Join Date
    Feb 2008
    Location
    adelaide sth.oz
    Posts
    1,015
    Rep Power
    19

    Re: Need answers on a freezer....

    heat exchanger on evap internal split ?
    mmm to beer or not to beer...........lets drink breakfast

  16. #16
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    37

    Re: Need answers on a freezer....

    Way back you did a compressor check, and acheived a 2inch vacuum. Something wrong there, I am not familiar with compressor, but maybe an internal relief is bypassing.
    OK with a suction gauge on service port and you close the suction valve the compressor suction should invert itself to a low vacuum.
    If the bypass is passing you are a mission to nowhere.

  17. #17
    Join Date
    May 2006
    Location
    USA
    Age
    50
    Posts
    14
    Rep Power
    0

    Re: Need answers on a freezer....

    Low cool- No heat exchanger.

    Magoo-This is a brand new compressor. And do the Copeland K bodies have an internal bypass? I don't believe they do? I believe the suction pressure would change if it was bypassing.

  18. #18
    Join Date
    Apr 2008
    Location
    phillippines
    Posts
    125
    Rep Power
    17

    Re: Need answers on a freezer....

    ToddH,

    Thinking that you have a blown gasket around valve plate assembly.
    abet

  19. #19
    Join Date
    May 2006
    Location
    USA
    Age
    50
    Posts
    14
    Rep Power
    0

    Re: Need answers on a freezer....

    I got the measurements today and I did it 2 ways. The first batch of numbers are with the evap fans off on fan delay. The second group is the the fan delay jumped out. Here's what I came up with.

    Unit started at 1:16 pm. Unit was running 20 minutes when these numbers were taken.

    92*f box
    98*f ambient

    Cond in:92*f
    cond out:110*f
    High Side pressure:310 lbs.
    Liquid line temp @ reciever:100*-114*f
    Low side psi: 40lbs.
    Suction line temp @TXV bulb:6*f

    30 minutes later, still with no fans.

    65*f box temp
    98*f amient

    Cond in temp: 98*f
    Cond out temp 107*f
    High side pressure:290lbs
    Liquid line temp @ Reciever 99*-108*f
    Low side psi: 33lbs
    Suction Temp: 1.6*f


    Here are the numbers with the fan delay jumped.

    Unit started at 2 pm.

    72*f box temp
    99*f ambient

    Cond in temp:98*
    Cond temp out: 112*
    High side psi: 310lbs
    Liquid line temp @ reciever outlet: 114*

    Evap air in:71*f
    Evap air out:68.4*f
    Low side pressure:48 lbs.
    Suction line temp @ TXV bulb:70.5

    Last numbers taken at 3:30 pm.

    53*f box temp
    99* ambient

    Cond temp in: 100*
    Cond temp out: 112.7*
    Highside psi: 310lbs
    Liquid line temp @ reciever outlet: 114.3*f

    Evap air in: 55*f
    Evap air out: 53.5*f
    Low side psi: 45lbs
    Suction line temp @ TXV bulb:54.5

    Hopefully I have everything you needed to kind of help steer me into some direction on this thing. This is the 1st one thats ever stumped me. Hopefully I can understand the terms because you fellas are alot more educated on this than I am! Thanks again...

    Todd

  20. #20
    Join Date
    Feb 2008
    Location
    adelaide sth.oz
    Posts
    1,015
    Rep Power
    19

    Re: Need answers on a freezer....

    ok fellas why the high head pressure if comp is stuffed unless hes converting discharge temperature to pressure
    mmm to beer or not to beer...........lets drink breakfast

  21. #21
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Need answers on a freezer....

    Is the new TXV an exact replacement? Same model numbers as the old TXV?

  22. #22
    Join Date
    May 2006
    Location
    USA
    Age
    50
    Posts
    14
    Rep Power
    0

    Re: Need answers on a freezer....

    Lowcool- no conversion on the pressure.

    Gary-This particular TXV no it's not. I went with the exact one before and it wasn't feeding enough either. This one was recommended for me to try.

  23. #23
    Join Date
    Mar 2007
    Location
    USA
    Posts
    118
    Rep Power
    18

    Re: Need answers on a freezer....

    If U are certain the evap and the dist tubes are free of obstruction it would surely seem to be the TXV from your numbers

  24. #24
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    37

    Re: Need answers on a freezer....

    If the compressor sucks a blind suction to 2inch vac.., there is a problem with bypass somewhere. Your call as to where.

  25. #25
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Need answers on a freezer....

    Quote Originally Posted by ToddH View Post
    Lowcool- no conversion on the pressure.

    Gary-This particular TXV no it's not. I went with the exact one before and it wasn't feeding enough either. This one was recommended for me to try.
    What were the original numbers?

  26. #26
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Need answers on a freezer....

    I have been searching for information on the ZP charge. They just say that it is a pressure limiting charge. Nobody is saying what pressure it is limited to.

  27. #27
    Join Date
    Feb 2008
    Location
    adelaide sth.oz
    Posts
    1,015
    Rep Power
    19

    Re: Need answers on a freezer....

    magoo it does sound inefficient but if blowpass is there,why the exceptional head pressure whilst running yet suction pressure is down.maybe non condensables or a roosters bum feathers in the system and a possible restriction in the liquid phase of condensing,maybe pump compressor down a couple of times to see if better than 2" can be achieved with a different set of clocks and leave to see if it holds it.only mentioned that if temp was converted to pressure it could be mistaken for heat of compression.whilst system has been recovered for non condensables fit a DANFOSS valve rated to coil and reprocess system with a different bottle of refrigerant.
    Last edited by lowcool; 07-07-2009 at 05:41 AM. Reason: forgot bum feathers
    mmm to beer or not to beer...........lets drink breakfast

  28. #28
    Join Date
    May 2006
    Location
    USA
    Age
    50
    Posts
    14
    Rep Power
    0

    Re: Need answers on a freezer....

    I will get the #'s off the old TXV tomorrow. I had a manager of my wholesaler talk to an engineer for their company and he said they were supposed to be limited to 35-40 lbs. The reason I had him call was I had seen 50-55 lbs at times. That's the other reason i haven't set super heat. I have to get the box cold enough to get off of the MOP of the valve to set it.

  29. #29
    Join Date
    May 2006
    Location
    USA
    Age
    50
    Posts
    14
    Rep Power
    0

    Re: Need answers on a freezer....

    Lowcool-I've used a couple of diff pair of guages to make sure mine were working correctly. The compressor will pull very little vacuum, but it will hold. It will pull a 29 inch vacuum with no head against it. I also used a different bottle of 404a when I recharged it thinking It was a crazy batch of gas but it changed nothing either.

  30. #30
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Need answers on a freezer....

    Quote Originally Posted by ToddH View Post
    Highside psi: 310lbs
    Liquid line temp @ reciever outlet: 114.3*f
    Ahaaaa...

    R404A @ 310 psi = 120F

    120 - 114 = 6F subcooling.

    Add refrigerant until the subcooling is 15F. That clear sightglass must be an empty sightglass.

    And that 310psi should be up around 350psi for a heavy load in 100F ambient.
    Last edited by Gary; 07-07-2009 at 06:02 AM.

  31. #31
    Join Date
    Feb 2008
    Location
    adelaide sth.oz
    Posts
    1,015
    Rep Power
    19

    Re: Need answers on a freezer....

    when checking superheat across the evap is the outlet colder or warmer than the inlet temperature
    mmm to beer or not to beer...........lets drink breakfast

  32. #32
    Join Date
    May 2006
    Location
    USA
    Age
    50
    Posts
    14
    Rep Power
    0

    Re: Need answers on a freezer....

    Gary- the original TXV was a FSE-1/2-ZP. And this thing has had a clear sight glass all along running 310 PBS of head pressure.

  33. #33
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Need answers on a freezer....

    Clear sightglass or not, the subcooling says it is undercharged.

  34. #34
    Join Date
    May 2006
    Location
    USA
    Age
    50
    Posts
    14
    Rep Power
    0

    Re: Need answers on a freezer....

    how do I figure subcooling so I can get to that magic number?

  35. #35
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Need answers on a freezer....

    Quote Originally Posted by ToddH View Post
    how do I figure subcooling so I can get to that magic number?
    Find the saturated condensing temperature (SCT) by converting high side pressure to temperature with a P/T chart.

    Measure the liquid line temperature near the receiver outlet.

    SCT minus liquid line temp = subcooling

  36. #36
    Join Date
    May 2006
    Location
    USA
    Age
    50
    Posts
    14
    Rep Power
    0

    Re: Need answers on a freezer....

    So I keep adding gas til 15 is achieved? I'll report back tomorrow! thanks again.

  37. #37
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Need answers on a freezer....


  38. #38
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Need answers on a freezer....

    Quote Originally Posted by ToddH View Post
    So I keep adding gas til 15 is achieved? I'll report back tomorrow! thanks again.
    Yes... until the difference between those two temps is 15F.
    Last edited by Gary; 08-07-2009 at 04:44 AM.

  39. #39
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Need answers on a freezer....

    Any progress today?

  40. #40
    Join Date
    May 2006
    Location
    India
    Age
    74
    Posts
    399
    Rep Power
    18

    Re: Need answers on a freezer....

    Compressor :
    Is there a way you can check up leak back of valve plate ( valve reeds ) on compressor ? Or ask copeland to supply these numbers . Probably reed leak back could be an issue.

  41. #41
    Join Date
    Sep 2005
    Location
    Australia
    Posts
    21
    Rep Power
    0

    Re: Need answers on a freezer....

    Hey Gary

    Can I just ask how you came about to decide that this system needed 15k subcooling. Is there a formula to be used that will decide upon the most efficient subcooling figure ?
    In the past I have always worked on 4 - 6k subcooling, but recently I found that I had greater performance with 12 - 16 k subcooling, however I am not sure how the systems will handle 40+ deg C ambient.

    Thanks

    Rooboy
    'Pipe Benders ?' 'Never heard of 'em'

  42. #42
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Need answers on a freezer....

    Quote Originally Posted by rooboy View Post
    Hey Gary

    Can I just ask how you came about to decide that this system needed 15k subcooling. Is there a formula to be used that will decide upon the most efficient subcooling figure ?
    In the past I have always worked on 4 - 6k subcooling, but recently I found that I had greater performance with 12 - 16 k subcooling, however I am not sure how the systems will handle 40+ deg C ambient.

    Thanks

    Rooboy
    That's 15F, not 15K.

    15F/8.5K is the maximum subcooling without backing liquid up into the condenser and raising high side pressure.

    There have been situations where the liquid needed to pump upwards to the evaporator and I have gone as high as 20F/11K subcooling to avoid flashing at the TXV, but that's pushing it.
    Last edited by Gary; 10-07-2009 at 04:05 AM.

  43. #43
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    37

    Re: Need answers on a freezer....

    Did you vapour or liquid charge R404A into system after changes.
    magoo

  44. #44
    Join Date
    Sep 2005
    Location
    Australia
    Posts
    21
    Rep Power
    0

    Re: Need answers on a freezer....

    Gary

    Thanks.

    I'll start another thread just on subcooling and get everyone's thoughts

    Rooboy
    'Pipe Benders ?' 'Never heard of 'em'

  45. #45
    Join Date
    Nov 2007
    Location
    USA
    Posts
    17
    Rep Power
    0

    Re: Need answers on a freezer....

    Id think that the system is over charged and the condenser and evaporator becomes part of the receiver device

Similar Threads

  1. Blast Freezer Within Freezer
    By rickmor in forum Technical Discussions
    Replies: 4
    Last Post: 18-06-2009, 03:37 AM
  2. ice cream truck freezer
    By GaryC in forum Transport
    Replies: 7
    Last Post: 06-12-2008, 02:19 AM
  3. Hotpoint FFA71 Freezer High Temp Light / Fridge is Freezing
    By sumnerpa in forum Trouble Shooting
    Replies: 1
    Last Post: 19-08-2008, 03:16 PM
  4. Freezer compressor running 20 Hours/day
    By rickcw in forum Domestic
    Replies: 12
    Last Post: 08-03-2008, 11:50 PM
  5. Trolley freezer & blast freezer
    By smpsmp45 in forum NH3
    Replies: 0
    Last Post: 25-08-2007, 07:29 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •