    Actually, even on service calls where there are cooling problems the ductwork should have a quick Manual D performed.

    Then take the ESP static pressure & compare to blower graph or chart, also take the FPM duct velocity.

    Then do a quick estimate of airflow per equipment tonnage.

    To find area of a round duct; Duct diam is 7"; 7"X7"= 49-sq.ins., X's .7854 = 38.04845-sq.ins divided/ by 144= 0.2672541-sq.ft. area X's FPM Velocity 550-FPM = 160.35246-CFM X30 = 4,810.5738 each 7" run X's 6 branch runs = 28,863-BTUH, or airflow for 2.4-ton.

    That would also be good for 2-ton; at 550-FPM velocity X's 0.2672541= 147-CFM X 30 = 4,410-BTUH each run X 6-runs = airflow for 26,460-BTUH.

    Never sell units requiring more airflow than the duct system & blower will support! - udarrell



  2. #2
    Join Date
    Apr 2009
    Location
    WI USA
    Posts
    27
    Rep Power
    0

    Re: Quick Check for Sizing Units to enough Airflow

    Quote Originally Posted by udarrell View Post
    Quick Check for Sizing Units to enough Airflow

    Actually, even on service calls where there are cooling problems the ductwork should have a quick Manual D performed.

    Then take the ESP static pressure & compare to blower graph or chart, also take the FPM duct velocity.

    Then do a quick estimate of airflow per equipment tonnage.

    To find area of a round duct; Duct diam is 7"; 7"X7"= 49-sq.ins., X's .7854 = 38.04845-sq.ins divided/ by 144= 0.2672541-sq.ft. area X's FPM Velocity 600-FPM = 160.35246-CFM X30 = 4,810.5738 each 7" run X's 6 branch runs = 28,863-BTUH, or airflow for 2.4-ton.

    That would also be good for 2-ton; at 550-FPM velocity X's 0.2672541= 147-CFM X 30 = 4,410-BTUH each run X 6-runs = airflow for 26,460-BTUH.

    Never sell units requiring more airflow than the duct system & blower will support! - udarrell
    I re-figured the top one from 550-FPM to 600-FPM Velocity, & forgot to change it to 600-FPM. (Corrected)
    - udarrell

Similar Threads

  1. Replies: 12
    Last Post: 27-03-2011, 04:12 AM
  2. Vrv
    By tgoonter in forum Air Conditioning
    Replies: 4
    Last Post: 11-01-2011, 06:25 AM
  3. AHU Calculations
    By SUBCONTRACTOR in forum Fundamentals
    Replies: 20
    Last Post: 07-11-2009, 04:51 AM
  4. New Building, New Units!!!
    By Fett in forum Air Conditioning
    Replies: 6
    Last Post: 19-11-2008, 03:43 PM
  5. Air conditioning maintenance procedure
    By Andy T in forum Air Conditioning
    Replies: 12
    Last Post: 27-05-2006, 06:57 PM

Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •