    Daikin FDYQ250M



    Hi everyone. I am new to the forum and i have just had installed a Daikin FDYQ250M ducted unit. What has happened is my neighbour is complaining that the external fan noise is too loud and annoys them. i've heard it inside their house,and with a window open it's no louder than a fan on high. Anyway I have contacted Daikin plus the installer and been told the unit can be programed to learn how it's used to adjust the outside unit fan speed to slow down during night. Basically my installer is taking considerable time get back to me as say he's waiting to get more info from Daikin. Daikin tell me that he could get the info staright away. I am wondering if there is any where I can get these instuctions to do myself before the noise issue esculates.

    thanks



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Daikin FDYQ250M

    Hi Carl, sorry can't find that model reference on the Daikin site.

    Do you have the model of the outdoor unit?
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Mar 2009
    Location
    KZN, South Africa
    Age
    64
    Posts
    2,212
    Rep Power
    20

    Re: Daikin FDYQ250M

    Could you install a condensing unit air deflector, like they do in parts of Asia?

    Perhaps this would deflect the sound so that it would become less of a nuisance.
    Engineering Specialist - Cuprobraze, Nocolok, CD Technology
    Rarefied Technologies ( SE Asia )

  4. #4
    carl's Avatar
    carl Guest

    Re: Daikin FDYQ250M

    thanks, going to get measurements and get one made up. Hopefully it'll reduce the noise

  5. #5
    carl's Avatar
    carl Guest

    Re: Daikin FDYQ250M

    the outdoor unit model number is RZYQ10PY1. thanks

  6. #6
    Join Date
    Mar 2007
    Location
    France
    Posts
    236
    Rep Power
    18

    Re: Daikin FDYQ250M

    Hi
    You will need an option pcb like DTA104A on the outdoor unit to reduce the noise level as well and / or reduce the power (demand control) this will lead an extra service cost...
    rgds
    cool#9

  7. #7
    carl's Avatar
    carl Guest

    Re: Daikin FDYQ250M

    thanks. I have installed a deflector and it appears to have reduced the noise. No complaints so far so hoping all is good now. I will look into the DTA104A in case i need to do this later. Thanks for all the advise given

    carl

  8. #8
    Join Date
    Nov 2007
    Location
    London
    Posts
    461
    Rep Power
    17

    Re: Daikin FDYQ250M

    you will be able to use the night quiet mode on the controller or you could input the low noise setting on the outdoor pcb.
    you should have a little picture on your controller with a picture of a house and a face.
    Pushing this button reduce your fan speed outside and the compressor speed.

Similar Threads

  1. Daikin not working... many problems
    By stankovicv in forum Air Conditioning
    Replies: 26
    Last Post: 11-12-2010, 09:01 AM
  2. Daikin AC parts from UK
    By skel00 in forum Air Conditioning
    Replies: 5
    Last Post: 05-04-2009, 01:24 PM
  3. Fixing Daikin A3 Error
    By Stuffy in forum Air Conditioning
    Replies: 3
    Last Post: 27-03-2009, 06:02 AM
  4. Daikin Comp and inverter
    By WCC73 in forum Air Conditioning
    Replies: 5
    Last Post: 08-11-2008, 08:44 PM
  5. Getting a price from Daikin....
    By monkey spanners in forum Chit Chat & Service Stories
    Replies: 4
    Last Post: 17-08-2008, 09:46 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •