    Hi guys, can anyone help i have a walk in freezer, Compressor is Lun'te R404A, CAJ2464Z Low side 40psi, high side 450psi, keeps going out on high pressure switch, only -8c to -10c.
    if any one can help me i will be very gratfull thanks



  2. #2
    jeds1972's Avatar
    jeds1972 Guest

    Re: walk in freezer

    Hi ,
    For what you say i think that the system has to much refrigerant ,working with R404a and being a Freezer the suction should be around -28 to achive a room temperature of -20.
    Try to recover some refrigerant or compressor is to small in capacity.

  3. #3
    Join Date
    Jul 2009
    Location
    london
    Posts
    11
    Rep Power
    0

    Re: walk in freezer

    someone top it up about 1month ago, also some fitted new compressor about 10 months ago maybe its to small, i will recover the refrigerant and re-charge the system, Thanks Jeds...

  4. #4
    Join Date
    Dec 2007
    Location
    lebanon
    Posts
    130
    Rep Power
    17

    Re: walk in freezer

    hi
    can u please give the size of this walk in and the metering device more info more help

  5. #5
    Join Date
    Jun 2005
    Location
    Stoke on Trent
    Age
    62
    Posts
    588
    Rep Power
    19

    Re: walk in freezer

    I fitted the same comp on a freezer room this morning, I find that condensers always seem too small on R404a equipment in my opinion, is it a package like a Williams or a Foster or is it a traditional evaporator with a remote unit. If it was me I would first off blow the condenser out with my air compressor even if it does look clean, if this does not help resize the room and make sure the equipment is the correct size, if it is I would then reclaim all the gas, vac it out and recharge it the reason been someone could of "topped it up" and as it is a blend the make up is critical, it seems even more critical on low temperature applications from my experience.

  6. #6
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: walk in freezer

    Quote Originally Posted by fridge 09 View Post
    someone top it up about 1month ago, also some fitted new compressor about 10 months ago maybe its to small, i will recover the refrigerant and re-charge the system, Thanks Jeds...
    An undersized compressor will have the same symptoms as an inefficient compressor (low head, high suction). I would be betting on overcharge.

  7. #7
    Join Date
    Jul 2009
    Location
    london
    Posts
    11
    Rep Power
    0

    Re: walk in freezer

    thanks for you're help guys, the system is a package job Lun'te the condenser unit is out side the type with a dog kennel over it, the freezer is about 3mtr x 1 1/2mtr approx, pipe run about 10mtrs i would say

  8. #8
    Join Date
    Dec 2007
    Location
    lebanon
    Posts
    130
    Rep Power
    17

    Re: walk in freezer

    hi fridge
    ur compressor is ok if the product entering the room is frozen but if its fresh it became too small
    if the product entering is frozen u must check ur metering device small orifice dirty condenser etc

  9. #9
    Join Date
    May 2006
    Location
    India
    Age
    74
    Posts
    399
    Rep Power
    18

    Re: walk in freezer

    Is the condenser selected for pull down condition ?

Similar Threads

  1. walk in freezer
    By ail in forum Refrigerants
    Replies: 8
    Last Post: 29-11-2009, 11:44 PM
  2. help!! getting beat up by a walk in freezer
    By avalanche in forum Commercial
    Replies: 12
    Last Post: 05-12-2008, 02:56 AM
  3. superheating 5-8 dc right for walk in freezer r404
    By przemo2 in forum Technical Speculations
    Replies: 3
    Last Post: 09-03-2008, 01:56 PM
  4. walk in freezer refrigeration sizing?
    By trammd in forum Technical Discussions
    Replies: 10
    Last Post: 02-11-2006, 11:56 AM
  5. It's snowing in my walk in freezer!
    By Matt in forum Commercial
    Replies: 19
    Last Post: 14-10-2006, 07:07 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •