Thread: R408 causing blocked drier?
02-07-2009, 07:57 AM #1
We converted an old R502 low temp freezer to R408 and since then we have had issues with the single core drier blocking up with fine brown dust? We have been forced to change it weekly and the quantity of the dust seems to be getting worse? Does the 408 clean up the system causing this dust to block up the drier?
02-07-2009, 08:03 AM #2
Re: R408 causing blocked drier?
Three thoughts:
1. Is the filter-drier breaking down internally?
2. Is this a corrosion deposit eg. rust, coming off some parts?
3. How well did you flush during the conversion?Engineering Specialist - Cuprobraze, Nocolok, CD Technology
02-07-2009, 08:54 AM #3
The drier physically is good.
There was no flushing. It was a room that could not be shut down for too long. It had a leak which was repaired and 408 was dropped in.
It looks like fine brown dust.
02-07-2009, 10:39 AM #4
Source: Bitzer Refrigeration Report - 15. Edition - A-501-15
Section: ...substitutes for R502
Page 15
Due to the good solubility characteristics of R22 and R290 an increased danger exists, that after conversion of the plant, possible deposits of oil decomposition products containing chlorine may be dissolved and find their way into the compressor and regulating devices.
Before conversion generously dimensioned suction gas filters and liquid line driers should therefore be fitted for cleaning and after approximately 100 hours operation an oil change should be made; further checks are recommended.Last edited by desA; 02-07-2009 at 11:01 AM.
02-07-2009, 09:51 PM #5
Thanks DesA
Thats a good find!
03-07-2009, 04:49 AM #6
^ It's a pleasure...
Blocked driers
By monkey spanners in forum Technical DiscussionsReplies: 13Last Post: 03-07-2008, 05:55 PM -
suction line drier.
By Joeheath in forum Air ConditioningReplies: 5Last Post: 10-04-2008, 08:59 PM -
blocked drier
By monkey spanners in forum Technical DiscussionsReplies: 4Last Post: 14-09-2007, 11:13 PM -
Shelf life of an uncapped dessicant drier.
By eberg in forum Air ConditioningReplies: 2Last Post: 22-08-2001, 01:22 PM -
Drier Position
By subzero*psia in forum CommercialReplies: 8Last Post: 23-07-2001, 10:28 PM