    R408 causing blocked drier?



    We converted an old R502 low temp freezer to R408 and since then we have had issues with the single core drier blocking up with fine brown dust? We have been forced to change it weekly and the quantity of the dust seems to be getting worse? Does the 408 clean up the system causing this dust to block up the drier?



  2. #2
    Join Date
    Mar 2009
    Location
    KZN, South Africa
    Age
    64
    Posts
    2,212
    Rep Power
    20

    Re: R408 causing blocked drier?

    Three thoughts:

    1. Is the filter-drier breaking down internally?
    2. Is this a corrosion deposit eg. rust, coming off some parts?
    3. How well did you flush during the conversion?
    Engineering Specialist - Cuprobraze, Nocolok, CD Technology
    Rarefied Technologies ( SE Asia )

  3. #3
    Join Date
    Apr 2008
    Location
    Tasmania
    Posts
    216
    Rep Power
    18

    Re: R408 causing blocked drier?

    The drier physically is good.

    There was no flushing. It was a room that could not be shut down for too long. It had a leak which was repaired and 408 was dropped in.

    It looks like fine brown dust.

  4. #4
    Join Date
    Mar 2009
    Location
    KZN, South Africa
    Age
    64
    Posts
    2,212
    Rep Power
    20

    Re: R408 causing blocked drier?

    Source: Bitzer Refrigeration Report - 15. Edition - A-501-15
    Section: ...substitutes for R502

    Page 15
    Due to the good solubility characteristics of R22 and R290 an increased danger exists, that after conversion of the plant, possible deposits of oil decomposition products containing chlorine may be dissolved and find their way into the compressor and regulating devices.
    Page 16
    Before conversion generously dimensioned suction gas filters and liquid line driers should therefore be fitted for cleaning and after approximately 100 hours operation an oil change should be made; further checks are recommended.
    Last edited by desA; 02-07-2009 at 11:01 AM.
    Engineering Specialist - Cuprobraze, Nocolok, CD Technology
    Rarefied Technologies ( SE Asia )

  5. #5
    Join Date
    Apr 2008
    Location
    Tasmania
    Posts
    216
    Rep Power
    18

    Re: R408 causing blocked drier?

    Thanks DesA

    Thats a good find!

  6. #6
    Join Date
    Mar 2009
    Location
    KZN, South Africa
    Age
    64
    Posts
    2,212
    Rep Power
    20

    Re: R408 causing blocked drier?

    ^ It's a pleasure...
    Engineering Specialist - Cuprobraze, Nocolok, CD Technology
    Rarefied Technologies ( SE Asia )

Similar Threads

  1. Blocked driers
    By monkey spanners in forum Technical Discussions
    Replies: 13
    Last Post: 03-07-2008, 05:55 PM
  2. suction line drier.
    By Joeheath in forum Air Conditioning
    Replies: 5
    Last Post: 10-04-2008, 08:59 PM
  3. blocked drier
    By monkey spanners in forum Technical Discussions
    Replies: 4
    Last Post: 14-09-2007, 11:13 PM
  4. Shelf life of an uncapped dessicant drier.
    By eberg in forum Air Conditioning
    Replies: 2
    Last Post: 22-08-2001, 01:22 PM
  5. Drier Position
    By subzero*psia in forum Commercial
    Replies: 8
    Last Post: 23-07-2001, 10:28 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •