02-07-2009, 06:11 AM #1
PUMY-P48NHMU errpr code
Hi;
I have the above unit installed in my home with 8 indoor units. I am getting an error code 5101. The system is running but seems to short cycle. The installer has not been of much help. Am now running two hour cooling test. What readings should I be looking for? looking for expert to make sure system is optimized.
Thanks
Michael
-
02-07-2009, 10:27 PM #2
Re: PUMY-P48NHMU errpr code
All the fault codes starting with 51 relate to temperature sensor faulure
open or closed circuit.
5101 is the fault code for the indoor units return air sensor Th21
and or
the outdoor unit TH4 temperature sensor.
If you have full fuction remote controller it will also display the address of the unit which has the faulty temperature sensor with the fault code.
The temperature sensors need to be checked for correct resistance
20 deg C = 6.3 ohms
30 deg C = 4.3 ohms
My son could do this when he was about 13 years old & doing electronics technology at school.
Suspect your air conditioning contractor needs payment or training.
-
03-07-2009, 02:20 AM #3
-
03-07-2009, 07:53 AM #4
Re: PUMY-P48NHMU errpr code
When you set the 2hr test run that just makes the system run flat out in the mode you set for two hrs.
The system will report any faults during this period the same as during normal operation.
The test run function helps the a/c engineer as he can monitor the system operation & take temperature / pressure / amps readings while the system is operating at forced max performance.
Based on the data collected the a/c engineer can then judge if the system has correct cooling / heating performance. Then if there is any poor performance he can investigate further.
If your system continues to report a 5101 fault then the temperature sensors need to be checked.
If the system has just been installed then fare chance the sensor is not plugged into the circuit board correctly. This can accidently happen when the installation enginner is making wiring connections & the sensor cables get disturbed. So it could be as simple as plugging the sensor back into its place at the circuit board.
Similar Threads
-
Mitsubishi PUMY P125Y error code 4250
By gjp in forum Air ConditioningReplies: 17Last Post: 04-03-2011, 10:23 AM -
Sanyo Text Back Fault Code Service
By techguy in forum Air ConditioningReplies: 1Last Post: 04-02-2009, 06:57 PM -
lennox fault code
By richelli in forum Trouble ShootingReplies: 0Last Post: 01-02-2008, 09:13 PM -
A6 Fault Code Problem
By markcubed in forum Air ConditioningReplies: 3Last Post: 29-12-2007, 11:29 AM -
mitsubishi city multi fault code
By robin r33 gtr in forum Air ConditioningReplies: 5Last Post: 05-11-2007, 10:23 PM