    PUMY-P48NHMU errpr code



    Hi;

    I have the above unit installed in my home with 8 indoor units. I am getting an error code 5101. The system is running but seems to short cycle. The installer has not been of much help. Am now running two hour cooling test. What readings should I be looking for? looking for expert to make sure system is optimized.

    Thanks

    Michael



  2. #2
    Join Date
    Mar 2007
    Location
    Warwickshire UK
    Posts
    723
    Rep Power
    21

    Re: PUMY-P48NHMU errpr code

    All the fault codes starting with 51 relate to temperature sensor faulure
    open or closed circuit.

    5101 is the fault code for the indoor units return air sensor Th21
    and or
    the outdoor unit TH4 temperature sensor.
    If you have full fuction remote controller it will also display the address of the unit which has the faulty temperature sensor with the fault code.

    The temperature sensors need to be checked for correct resistance
    20 deg C = 6.3 ohms
    30 deg C = 4.3 ohms

    My son could do this when he was about 13 years old & doing electronics technology at school.

    Suspect your air conditioning contractor needs payment or training.

  3. #3
    kidcurry's Avatar
    kidcurry Guest

    Re: PUMY-P48NHMU errpr code

    Quote Originally Posted by Thermatech View Post
    All the fault codes starting with 51 relate to temperature sensor faulure
    open or closed circuit.

    5101 is the fault code for the indoor units return air sensor Th21
    and or
    the outdoor unit TH4 temperature sensor.
    If you have full fuction remote controller it will also display the address of the unit which has the faulty temperature sensor with the fault code.

    The temperature sensors need to be checked for correct resistance
    20 deg C = 6.3 ohms
    30 deg C = 4.3 ohms

    My son could do this when he was about 13 years old & doing electronics technology at school.

    Suspect your air conditioning contractor needs payment or training.
    Thanks for the reply.

    I ran the 2 hour cooling test but nothing displayed at test end. Should there be a error code at the end of the test?

  4. #4
    Join Date
    Mar 2007
    Location
    Warwickshire UK
    Posts
    723
    Rep Power
    21

    Re: PUMY-P48NHMU errpr code

    When you set the 2hr test run that just makes the system run flat out in the mode you set for two hrs.

    The system will report any faults during this period the same as during normal operation.

    The test run function helps the a/c engineer as he can monitor the system operation & take temperature / pressure / amps readings while the system is operating at forced max performance.
    Based on the data collected the a/c engineer can then judge if the system has correct cooling / heating performance. Then if there is any poor performance he can investigate further.

    If your system continues to report a 5101 fault then the temperature sensors need to be checked.
    If the system has just been installed then fare chance the sensor is not plugged into the circuit board correctly. This can accidently happen when the installation enginner is making wiring connections & the sensor cables get disturbed. So it could be as simple as plugging the sensor back into its place at the circuit board.

Similar Threads

  1. Mitsubishi PUMY P125Y error code 4250
    By gjp in forum Air Conditioning
    Replies: 17
    Last Post: 04-03-2011, 11:23 AM
  2. Sanyo Text Back Fault Code Service
    By techguy in forum Air Conditioning
    Replies: 1
    Last Post: 04-02-2009, 07:57 PM
  3. lennox fault code
    By richelli in forum Trouble Shooting
    Replies: 0
    Last Post: 01-02-2008, 10:13 PM
  4. A6 Fault Code Problem
    By markcubed in forum Air Conditioning
    Replies: 3
    Last Post: 29-12-2007, 12:29 PM
  5. mitsubishi city multi fault code
    By robin r33 gtr in forum Air Conditioning
    Replies: 5
    Last Post: 05-11-2007, 11:23 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •