    3 phase 220v



    I have a customer who has bought a 220v 3 phase heat pump. I have never come across 220v 3 phase and I have spoken to a few electricians who know nothing about it either. Other than using some sort of transformer/converter surely it is not possible to use this in this country(ENGLAND). Has anyone else had any experience with 220v 3 phase rather than 415v 3 phase. There is also no neutral on the Heat Pump. I think these are perhaps for the European/American market and he has been sold the wrong unit. Thanks



  2. #2
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: 3 phase 220v

    Quite common power supply in Norway and some other countries, like USA.
    Infact the 120 Vac single phase is derived from 220 Vac three phases.
    Neutral is not required.

    You may still use it by purchasing a 415/230 three phase autotransformer. It doesn't come cheap, though.

  3. #3
    Join Date
    May 2008
    Location
    Belgium
    Age
    66
    Posts
    802
    Rep Power
    16

    Re: 3 phase 220v

    you can change it in a mono 220V ,but you need a condensator to create a thirt line but loose a lot of power, aprox 1/3.
    in Belgium we have all of this , mono 220V, 3 fase 220V and 3+1(N) 399V or 400V as they say. it is possible to make from 3 fase 22OV a mono 220V but would not recomand it. it is easyer from 40OV. just watch out for the allignment L1/L2/L3 or the motor is turning the wrong way and cracks to pieces.
    Ice

  4. #4
    canadian tec's Avatar
    canadian tec Guest

    Re: 3 phase 220v

    I have a 220v 3 phase 8 hp low temp cooler runnining off a phase converter from Phase perfect out of the U.S. Installed now for 3 years not a min problem. It is possible, phase converter cost about $2500.00 US. Hope it helps...

  5. #5
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: 3 phase 220v

    Quote Originally Posted by icecube51 View Post
    you can change it in a mono 220V ,but you need a condensator to create a thirt line but loose a lot of power, aprox 1/3.
    I don't think this can be done. With a capacitor you will end up having two live conductors, not three.
    If the third is the neutral, then it won't work because the neutral is not live, and you can't pull current from it.

  6. #6
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: 3 phase 220v

    Used to deal with three phase 220v units on print machines in the past.

    Some sort of converter/transformer in line with the usual mains.

    Yes, he's been sold a pup.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  7. #7
    Join Date
    Aug 2008
    Location
    ENGLAND
    Age
    54
    Posts
    27
    Rep Power
    0

    Re: 3 phase 220v

    Thanks everyone. It looks as though the customer as been sold a unit that is not for use in this country, without altering the 3 phase incoming supply.

  8. #8
    Join Date
    Aug 2008
    Location
    Baltics
    Age
    62
    Posts
    786
    Rep Power
    16

    Re: 3 phase 220v

    But do at least frequencies coincide ?
    The 415V supply, of course, has neutral and there is 240V phase voltage at the client's place?

  9. #9
    Join Date
    Feb 2008
    Location
    USA
    Age
    51
    Posts
    10
    Rep Power
    0

    Re: 3 phase 220v

    Quote Originally Posted by canadian tec View Post
    I have a 220v 3 phase 8 hp low temp cooler runnining off a phase converter from Phase perfect out of the U.S. Installed now for 3 years not a min problem. It is possible, phase converter cost about $2500.00 US. Hope it helps...

    I thought Canada already have 220v/3phase like the US why are u still using a phase converter?

    I have been looking for someone who has successfully used one in the past. I want to use it for a 1200lb cube machine (Hoshi) i wanna get from ebay/any other auction. Want to use it in West Africa.

    More on your experience with the phase converter will be appreciated.

  10. #10
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: 3 phase 220v

    If your motor is internally (or in connection box) connected in delta, you could reconnect it in star and then connect it normally on 380-400V 3phase power supply.

    If motor windings are wound for 220V than this star connection would not mean less power.

    Question is if motor is suitable for 50Hz frequency.

    Could you post picture of motor/compressor nameplate or make and model# of compressor.
    Last edited by nike123; 02-07-2009 at 06:25 PM.

  11. #11
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    37

    Re: 3 phase 220v

    I go along with Brian_UK, your mate was sold a pup, tip it out and start again.
    Any add ons will mean more money that the system is worth.

  12. #12
    Join Date
    Aug 2008
    Location
    ENGLAND
    Age
    54
    Posts
    27
    Rep Power
    0

    Re: 3 phase 220v

    Yes I agree Magoo. Luckily the suppliers are changing it for a 3 phase 415v, free of charge. Good old Heat Perfector.
    Thanks everyone.

  13. #13
    Join Date
    Mar 2007
    Location
    manchester
    Age
    17
    Posts
    63
    Rep Power
    19

    Re: 3 phase 220v

    but some big batteries?

  14. #14
    Join Date
    Feb 2005
    Location
    Hong Kong
    Posts
    190
    Rep Power
    20

    Re: 3 phase 220v

    If the supplier already offered to exchange, then problem solved.

    Otherwise refer to Nike123's good information on STAR-Delta reconfiguration possibilities. Check the motor plates in these situations. Dual range or dual voltage is many times possible.
    There are guidelines too on permissible Hertz variation with Voltage.

    regards
    T-P
    Remember what Augustus once said:
    "festina lente" - make haste, slowly!

  15. #15
    Join Date
    Dec 2007
    Location
    lebanon
    Posts
    130
    Rep Power
    17

    Re: 3 phase 220v

    hi
    if the component of this unit are working @220v such fans etc...easiest way change ur compressor hope this help

  16. #16
    Join Date
    Aug 2006
    Location
    Canada
    Age
    61
    Posts
    149
    Rep Power
    18

    Re: 3 phase 220v

    Quote Originally Posted by canadian tec View Post
    I have a 220v 3 phase 8 hp low temp cooler runnining off a phase converter from Phase perfect out of the U.S. Installed now for 3 years not a min problem. It is possible, phase converter cost about $2500.00 US. Hope it helps...
    I am not sure why this would be required as 220v 3 phase is normal in Canada. (we actually have 208v 3 phase, but compressors will tolerate this small a variance.)
    The compressor ratings that I have seen will tolerate 50 or 60 HZ.

  17. #17
    Join Date
    Sep 2009
    Location
    Iran
    Age
    66
    Posts
    672
    Blog Entries
    1
    Rep Power
    19

    Re: 3 phase 220v

    nik right, but look for control panel also it should be check .

Similar Threads

  1. 3 phase resistance calculation
    By bill1983 in forum Electrical
    Replies: 33
    Last Post: 05-10-2010, 08:23 PM
  2. single phase 208v
    By j.a.violante in forum Air Conditioning
    Replies: 2
    Last Post: 24-05-2009, 07:18 AM
  3. generic single phase contactor?
    By paul_h in forum Electrical
    Replies: 9
    Last Post: 06-02-2009, 08:28 AM
  4. SR2 50 models electric SBY diagonostics made simple
    By absolute-zero in forum Transport
    Replies: 5
    Last Post: 04-01-2008, 05:11 PM
  5. 3 phase connections
    By davidler in forum Industrial
    Replies: 2
    Last Post: 22-03-2004, 02:11 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •