    Trane Weathertron 900 XE wierd issue



    The compressor on my trane Weathertron 900 XE heat pump was replaced recently with the correct model and now is experiencing a wierd problem.

    While troubleshooting the earlier problem, the HVAC consultant made a number of wiring changes near the control board on the outside unit, replaced both run and start caps and eventually determined that the compressor was defective.

    The heatpump compressor and compressor fan start correctly from the inside thermostat but the compressor fan will stop running after 45-50 minutes. Subsequent to that the compressor will overheat and shutdown due to thermal overload. Once the heatpump cools down it does not restart automatically but will restart if the outside fuse is removed and reseated whereupon the compressor fan will again run 45-50 minutes before stopping while the compressor is running and the cycle continues.

    To resolve this condition, The HVAC consultant has replaced the compressor fan, thinking it was undergoing a heat related shutdown as well as checked discharge and return pressures and temps which are all normal. Replaced the filters inside the house, checked the air handler and just about everything else.


    I am not a HVAC guy but I think the issue is related to the wiring work that was done during the earlier diagnostic tests and that the heat pump is running a defrost cycle during normal AC operation. As In uderstand it, during cold winters when the heatpump is in heater mode, the fan will cycle off every 45-50 minutes to allow the compressor heat to melt accumulated ice to prevent ice buildup.

    Is there a way to test this or even better is there a way to determine if the wiring is correct as my options are to buy a new control board.

    any help appreciated,

    trader_Mike



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Trane Weathertron 900 XE wierd issue

    Is the unit running in cooling or heating mode when this problem occurs?

    It does sound suspicious though.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    trader_Mike's Avatar
    trader_Mike Guest

    Re: Trane Weathertron 900 XE wierd issue

    good question, I checked last night and the unit has exactly the same behavior when it is in heat or cool mode.

    I dont see how its possible for the unit to be wired correctly and have this problem. The more I research it the more I am of the opinion that its not wired correctly or in some defrost test mode, if thats even possible.


    trader_Mike

  4. #4
    Join Date
    Jul 2003
    Location
    caribbean
    Age
    74
    Posts
    8
    Rep Power
    0

    Re: Trane Weathertron 900 XE wierd issue

    probably repaired by now- if the capacitor were miswired, the motor would overheat faster than 45 to 50 minutes. Miswiring or bad capacitor are possible but my money is on worn motor bearings.

  5. #5
    trader_Mike's Avatar
    trader_Mike Guest

    Re: Trane Weathertron 900 XE wierd issue

    Quote Originally Posted by Brian_UK View Post
    Is the unit running in cooling or heating mode when this problem occurs?

    It does sound suspicious though.
    Its been a long time coming but the issue was resolved and we can close the X files on this one.

    Briefly,
    The original 7.5uF fan cap was replaced some time ago with a 10uF cap and that caused the fan to overheat. When the fan overheated, it stopped turning (thermal overload) and the Compressor overheated. It just so happened that the symptom looked like it was being caused by the heat pump entering defrost mode. Putting the correct fan cap in resolved the fan overheating issue.

    Again thanks

    Mike

  6. #6
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Trane Weathertron 900 XE wierd issue

    Thanks for the update Mike and glad to hear that the problem has been resolved.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

Similar Threads

  1. AEC Pinical chiller with trane comp
    By cptrdbrd in forum Commercial
    Replies: 1
    Last Post: 28-10-2009, 09:47 PM
  2. trane ertaa213 EEV fault (1AA)
    By knight rider in forum Technical Discussions
    Replies: 4
    Last Post: 11-06-2009, 06:40 AM
  3. New to Forum, Facing problems related with TRANE Chiller
    By neerajpuranik in forum Air Conditioning
    Replies: 3
    Last Post: 10-12-2008, 02:43 AM
  4. Trane CVHE 450 R11 Centrifugal Chiller
    By albertjoseph in forum Air Conditioning
    Replies: 4
    Last Post: 06-10-2008, 03:23 PM
  5. Trane Defrost Control Board Energize "W" in cooling
    By jcmorris2 in forum Heat Pumps
    Replies: 6
    Last Post: 02-06-2007, 03:40 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •