01-07-2009, 03:43 PM #1
Trane rtac 170
Hi,
I just had to get out of the sun for a couple of minutes as my client is going to wonder why my face is tanned and not the back of my neck!
I have a site with the above chiller, during the winter or prolonged periods of low demand, circuit number two fails on low oil pressure/flow, I can understand why as the compressor runs unloaded for extended periods of time, I left the circuit locked out on the control panel, I pumped the circuit down today and then ran it and monitored it carefully;
Sat. Suction = 4 Sat. Condensing = 39 SH = 5 SC = 6 Oil Pressure = 763 Kpa Oil Temp. = 54 Current = 92 95 98 %FLA = 57 59 60.
As you can see with enough load the circuit runs fine, what I cannot understand is why does circuit number one run "perfectly" all year round and cope with the variations in load? Could it be the way that the evaporator is designed?
Anyone else had the same?
Cheers
Tutto il Mondo e un Paese
-
01-07-2009, 10:40 PM #2
Re: Trane rtac 170
Hi, sounds like internal oil pressure relief valve is faulty. This is a repair that should be looked at by a local Trane Service Agency. Cheers.
-
03-07-2009, 07:06 AM #3
Re: Trane rtac 170
Thanks centrecipew,
I have changed oil filter, checked strainers on oil return lines etc. Shall suggest a Trane engineer, I did'nt want to miss something obvious.
CheersTutto il Mondo e un Paese
-
03-07-2009, 05:16 PM #4
Re: Trane rtac 170
What's the serial number and type, could be it was just not designed to work in low ambiant! Is the first fan stage y/delta or VSD?
-
06-07-2009, 06:02 PM #5
Re: Trane rtac 170
Hi Lowrider,
the model number just says RTAC 170, there are no other letters after the model number, I think that the fan stages are all DOL, there is definately no converter/inverter.
Thanks for replying
CheersLast edited by El Padre; 01-02-2010 at 05:05 PM.
Tutto il Mondo e un Paese
-
07-07-2009, 07:51 PM #6
Re: Trane rtac 170
Inside the panels there should be a long code starting with ERTAC170. There after start the option codes. Since it has no VFD it is not a Low Ambiant version.
Reasons why the compressor would shut down on low oil flow:
Could be the oil return from the bottom off the evaporator, there's a check valve in there.
The oil heater in the separator of that compressor could be working at a lower temperature or not producing enough heat!
Did you check to see if the intermediate oil pressure sensor is measuring correct all the time? If you run the unit in part load with a gauge on the oil line you'll be able to see if it doesn't.
Official explaination of the diagnostic:
The intermediate oil pressure transducer for this compressor was out
of the acceptable pressure range for 15 seconds, while the Delta
Pressure was greater than 35 Psid.: Acceptable range is 0.50 > (PC-PI)
/ (PC-PE) for the first 2.5 minutes of operation, and 0.25 > (PC-PI) / (PCPE)
thereafter,
Similar Threads
-
Trane RTAC 170 , Phase reversal trip?
By THE WOMBAT in forum CommercialReplies: 26Last Post: 09-07-2010, 01:23 AM -
AEC Pinical chiller with trane comp
By cptrdbrd in forum CommercialReplies: 1Last Post: 28-10-2009, 09:47 PM -
trane rtac 275
By anish in forum Air ConditioningReplies: 6Last Post: 01-10-2008, 10:24 PM -
Trane RTAC Software Download
By sean in forum CommercialReplies: 4Last Post: 30-09-2008, 12:36 PM -
Trane Defrost Control Board Energize "W" in cooling
By jcmorris2 in forum Heat PumpsReplies: 6Last Post: 02-06-2007, 03:40 AM