    humidity and ac



    Hi,

    Howcome everytime i turn on my ac, the level of humidity of the room is increase to 90%?

    Thanx!



  2. #2
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: humidity and ac

    When it is running does water come out of the condensate drain pipe?

  3. #3
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: humidity and ac

    Where are you measuring the humidity?

    What are the temperatures, wet and dry bulb, in the room before turning the unit on and when you consider that the RH has increased?
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  4. #4
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    37

    Re: humidity and ac

    If in cooling mode, the majority of modern air conditioners have a high SHF [sensible heat factor ] of approximately 85%, as in dry bulb temp reduction, so with a low latent cooling factor of balance at say 15 %, the moisture removel quantity is small.
    Therefore the wet bulb temperature does not reduce proportionally to dry bulb reduction, so guess what ... the Relative humidity rises.
    Inversly when heating, all the output is sensible heating, so dry bulb temp rises, and wetbuld is un-changed, so relative humidity is low and starts to dry interior of dwelling, sucks up moisture from everything trying to balance out DB and WB. Turn the heating off and interior ambients drops, condensation on all cold surfaces like windows etc., dew point acheived.
    A psychometric chart will explain everything.
    magoo

  5. #5
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: humidity and ac

    Quote Originally Posted by Magoo View Post
    A psychrometric chart will explain everything.
    Yep... Find your target room temp at the bottom of the psychrometric chart. Draw a vertical line up to the target room RH. Draw a horizontal line left to the 100%RH line. Then draw a vertical line down to find the coil leaving air temp needed to achieve the targets.

    If the leaving air temp is higher than this (when the room temp is at target), reduce the blower speed to lower the leaving air temp. Once the blower speed is adjusted, eventually the room will achieve both RH and temp targets.

    The downside is that this will lower the system efficiency. It takes energy to remove moisture from air.
    Last edited by Gary; 02-07-2009 at 04:27 AM.

  6. #6
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    37

    Re: humidity and ac

    Hi Gary.
    We are of similar vintage and probably similar training practices.
    Unfortunately these days with all the plug and play systems out of boxes, add that the young techs are not really familiar with real air conditioning systems, add economics as well. In my training days [ along time ago ] airconditioning meant, air filtration and quality, humidity control, and temperature control, ie ., enviroment control.
    All lost in space lately, temp control and minimal power consumption is the current criteria.
    Ask a young a/c tech about a psychometric chart and a blank look will be common.

    magoo

  7. #7
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: humidity and ac

    I agree, Magoo. The level of training these days just doesn't seem to be what it used to be.

  8. #8
    Join Date
    Apr 2009
    Location
    WI USA
    Posts
    27
    Rep Power
    0

    Re: humidity and ac

    I began as a tech in the first half of the 1970's; back then in the SW U.S., oversizing the equipment on undersized duct systems was a major problem. Nobody worried about energy usage.

    If you sized those babies right, on proper ductwork, they would flat-out - pull the humidity down big-time even at +400 & 450-CFM per-ton.

    They had oversized compressors to the condenser & the evaporator, you could get it close to freezing the condensate & that's why it needed more airflow per ton of cooling.

    Now, they have trouble getting the coil below the dew point, ha. Okay, in the desert, but so is a swamp cooler.

    I liked the 10 & 12-SEER units; there was no need for the govt to take them off the option table!

    There are high humidity situations where they could outperform these units, that too many can't afford to buy. - udarrell

Similar Threads

  1. High humidity comfort cooling
    By Thermatech in forum Air Conditioning
    Replies: 70
    Last Post: 27-11-2008, 01:01 AM
  2. Humidity reccomendations in offices
    By back2space in forum Air Conditioning
    Replies: 21
    Last Post: 22-10-2008, 10:23 PM
  3. Humidity Chamber - Please Help
    By Deejay in forum Technical Discussions
    Replies: 4
    Last Post: 29-09-2007, 03:17 AM
  4. removing humidity
    By Sledge in forum Air Conditioning
    Replies: 31
    Last Post: 22-06-2007, 05:40 AM
  5. Humidity
    By frank in forum Air Conditioning
    Replies: 20
    Last Post: 30-12-2002, 08:06 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •