    frascold compressor fault
    anybody got any ideas
    I have a frascold semi-hermetic compressor model 06VM306A badged as a Carrier compressor which was running pulling low amps, not pumping etc, etc.
    Stripped it down to find pistons, valves, crank and conrods all fine.
    Then found that i could spin the rotor around the crank shaft, so some how the rotor has come ditached from the crankshaft, i assume some sort of pin or key way must have broken.
    I haven't managed to pull the rotor out yet cause i don't know how to and didn't want to force it .
    Any help please.
    CB
    Mar 2006
    Merate (LC) - Italy
    2,549
    Re: frascold compressor fault
    Unscrew the bolt and remove it along with the washer/plate.
    Pull the rotor by hand or helping yourself with a plier. As easy as that.
    Or, more simply, just return it for replacement against a green Carrier badged or unbadged, genuine Frascold.
    Contact me via email at Frascold's customer care.
    Northants
    290
    Thanks mate, do you think a pin is broke then. Why is the rotor spinning with the crankshaft
    CB
    Oct 2006
    1,843
    21
    Quote Originally Posted by chillyblue View Post
    CB
    The crank will have a slot ground along it and the rotor has a matching slot init. When fitted together and in line they form a channel that a key (square bar about 2 inch long) is inserted to hold the two together.
    It is possible for this key to sheer but the force excerted to it to do so must have been huge.
    A new key can be obtained and inserted as described in the post above.
    Somthing caused it to fail though so you need to give it a good check before rebuilding.
    Cheers taz.
    Mar 2006
    Merate (LC) - Italy
    2,549
    I think it didn't break. Either it slipped out from the groove, or some idiotic moron just forgot to put it in.
    Funny enough, as the compressors are tested in nitrogen, the rotor has got enough shear to the shaft to pass the test run even if the key is not in the slot.
    Northants
    290
    Quote Originally Posted by NoNickName View Post
    this has run for years, i think the oil seperator float (no sol valve in return line to comp sump) has stuck open and gas has condensed in the compressor causing it to hydralic on start up (the client runs it for a periods and then leaves it switched off for long periods)
    I did take the back end bolt/washer out but couldn't pull the rotor out, i wasn't to force full in pulling it because i wasn't sure if there was anything else holding it in. perhaps i should be more forcefull????????
    CB
    Mar 2006
    Merate (LC) - Italy
    2,549
    Ok, that means the key was there.
    No, there's nothing else holding it, unless it seized on the shaft. But if so, how is it that you can spin it around, but it doesn't come off?
    Northants
    290
    It must be on a bearing or something because it is running totally smooth and totally free even if spun by hand it rotates without any effort.
    CB
    Mar 2006
    Merate (LC) - Italy
    2,549
    No, it's not on a bearing. I am from the manufacturer.
    Northants
    290
    Is there a service manual that explains the strip down you could send me??
    Also how do you remove the pistons/ conrods etc.
    Cheers for your help
    CB
    Mar 2006
    Merate (LC) - Italy
    2,549
    Please contact me off forum
    Oct 2006
    1,843
    21
    CB
    I bet you will find the crank has sheared just after the main bearing.
    That is why the rotor rotates without any effort.
    The crank will be held in place only by the front bearing.
    Needs a strip down to confirm but it looks like it needs another comp.
    taz.
    Northants
    290
    Quote Originally Posted by taz24 View Post
    taz.
    Can't be because i have took out the bolt at the motor end of the crank and had to hold the crank at the piston end, so the cranks not sheared.
    it's wierd because i can turn the crank from both ends, all the piston and con rods are fine.
    To me it just seems as though the rotor is a sleeve around the crankshaft but without any connection to the shaft.
    CB
    Auckland
    74
    3,357
    37
    Probably worn a step in shaft, so you are trying to pull against the step. Could be difficult to lift evenly and pull off at the same time.
    Hell send it back as a warranty claim.
    magoo
    Mar 2006
    Merate (LC) - Italy
    2,549
    magoo
    He could, although it looks like it ran for years.
  1. Where to get Frascold gaskets?
    By monkey spanners in forum Commercial
    Last Post: 28-02-2009, 11:35 PM
  2. Frascold and propane
    By ConDor in forum Hydrocarbons
    Last Post: 25-01-2008, 08:31 AM
  3. frascold compressor out of oil
    By DEVIL in forum Trouble Shooting
    Last Post: 25-07-2007, 06:58 PM
  4. Frascold screw manual
    By nh3tech in forum Industrial Compressors
    Last Post: 17-07-2007, 11:17 AM
  5. 8 cyl. Frascold