30-06-2009, 08:28 AM #1
Cvgd trouble
sorry about my english. i have trouble with my cvgd. indicated b E7. please help me
-
30-06-2009, 05:06 PM #2
Re: Cvgd trouble
What is a CVGD please?
Brian - Newton Abbot, Devon, UK
Retired March 2015
-
30-06-2009, 05:23 PM #3
-
30-06-2009, 09:20 PM #4
Re: Cvgd trouble
Hi,
bE7 is a high motor temperature fault indication.
Check the motor cooling line ( 1 1/8 ), the line running from the bottom of the condenser pot to the motor.
There is an inline filter, a temperature drop across this filter would indicate a blockage.
If the motor is still cool whilst running I would then suggest that you check the Thermistor Terminals in the small junction box between the rear of the motor and the condenser.
First Isolate the Main and control circuit supplies, then remove the small junction box cover.
Inside are 4 spade terminals. Check for continuity and balanced resistance across the terminals. 1 common and 3 Thermistor readings +- 75ohm @75F.
If any thermistor is open circuit this is your problem.
Good Luck
-
30-06-2009, 09:23 PM #5
Re: Cvgd trouble
Trane Water Cooled 2 stage Centrifugal Chiller.R134a /R12
-
01-07-2009, 05:26 AM #6
Similar Threads
-
Trouble shooting tx valves
By TECH TIM in forum Trouble ShootingReplies: 11Last Post: 01-02-2011, 05:13 PM -
books for Trane trouble shooting
By RobertK in forum Refrigeration BooksReplies: 11Last Post: 15-07-2009, 12:17 PM -
MD-II SR Trouble Codes
By lherring81 in forum TransportReplies: 8Last Post: 22-05-2009, 12:18 AM -
How to trouble shoot a system
By US Iceman in forum Trouble ShootingReplies: 12Last Post: 16-02-2007, 08:23 AM -
Trouble Shooting
By Vincent Yu in forum FundamentalsReplies: 20Last Post: 22-11-2005, 02:04 PM