    High Suction Temps



    Hi,

    Could anyone help me out, we have an NH3 system, single stage cooling glycol, (economised)
    glycol setpoint is @ -5 degrees,
    we run stal 71Es and have a howden 255

    On the Howden 255 the suction pressure is 212kPa
    and suction temperature of -6.6 at compressor
    however on the stal the suction pressure is the same(212) but the suction temperature is @ -3.3 at compressor

    Have checked temperature probe and all ok.

    any ideas?



  2. #2
    Join Date
    Dec 2007
    Location
    australia
    Posts
    3,355
    Rep Power
    39

    Re: High Suction Temps

    If the Stal is unloaded suction will be warmer due to internal bypass of gas and lower flow of gas going through comp .
    Is this the case ?
    Also may depend on location of temp sensor in suction line .

  3. #3
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: High Suction Temps

    Also, some compressor packages have the oil return from the separator dumping back into the suction valve. Under low capacity operation (unloaded) the higher oil temperatures mixing with reduced gas flow can increase the apparent suction temperature indicated. If the suction temperature comes back to what you would call normal when the compressor is fully loaded, I would not worry about it.
    If all else fails, ask for help.


  4. #4
    Join Date
    Jan 2008
    Location
    UK
    Posts
    16
    Rep Power
    0

    Re: High Suction Temps

    The compressor is running fully loaded, the PT100 is located on the suction housing, however I am more thinking that there is too much superheat as the VLR does run slighly short, and the gas is superheated before it arrives to the compressor,
    They are a Stal71E's and are in poor condition (approx 30 years old),
    Lately we have been having discharge temperature problems , hence whilst I think it may be due to excess superheat,

    The oil cooling system is thermosiphon controlled with a closed loop circuit with VSD drives on the condensor controling @ 10.5BARg, it seems that if we have all compressor running fully loaded (7 off)and one cycles off on temp that another compressor down the line will start alarming on High oil temp, its as if there is not enough liquid feeding the oil coolers after one or two compressors stop but the thermosiphon vessel is 3/4 full,
    I have also ensured that the valves are regulated from No.1 compressor through to No.7 ensuring equal amount of liquid to all oil coolers, there are no oil temperature control valves on the oil cool, just liquid inlet and outlet,

    Could anyone shed some light on this?

    Regards

  5. #5
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: High Suction Temps

    High suction temperatures at full load can certainly increase the discharge temperature. Especially if you are experiencing oil cooling issues also.

    I posted a short reply in the other thread you started.
    If all else fails, ask for help.


Similar Threads

  1. Sabroe CMO 26 high suction temperature
    By paddyraf in forum Air Conditioning
    Replies: 9
    Last Post: 25-01-2009, 03:49 AM
  2. Compressor loading, cooling, and range of operation.
    By Air duster in forum Fundamentals
    Replies: 10
    Last Post: 02-04-2008, 08:39 AM
  3. Benji
    By benji in forum Trouble Shooting
    Replies: 29
    Last Post: 30-01-2008, 01:25 PM
  4. SAB 110 Screw Compressor -High Suction Pressure
    By verstep in forum Industrial Compressors
    Replies: 5
    Last Post: 07-12-2006, 12:25 PM
  5. Replies: 10
    Last Post: 18-03-2006, 07:35 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •