Thread: air well ac

  1. #1
    Join Date
    Mar 2006
    Location
    belfast
    Posts
    239
    Rep Power
    19

    air well ac



    got a call to ac unit. found air on indoor 26c air of 9.1 but only cooling on 2 sides rather than all 4.
    air on condenser 21c air off 33c

    put gauges on suction 35psi head 200 psi r407c

    i suspected system short of gas. recovered 3.7kg should have been 3.8kg so nothing major with the gas.

    checked strainer on inlet to evap and it seemed ok.

    pressure tested and vaced out. only left for 30mins vac as it seemed to pull a good vac and i was busy

    weighed in new gas and ran system

    same problems as before low suction 35 to 40psi head pressure 200psi and indoor unit only cooling on 2 sides.


    so im wondering is this moisture rectriction or are my scales broken although have used them all week and theve been fine.

    any help would be great as this is a cash job and i have to pass this shop everyday on the way home so im going to be tourtured.
    thanks.



  2. #2
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: air well ac

    Quote Originally Posted by thebigcheese View Post
    only cooling on 2 sides rather than all 4.
    What does that mean?

  3. #3
    Join Date
    Mar 2006
    Location
    belfast
    Posts
    239
    Rep Power
    19

    Re: air well ac

    the cassette unit is only blowing cold from 2 sides rather than the four

  4. #4
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: air well ac

    Quote Originally Posted by thebigcheese View Post
    the cassette unit is only blowing cold from 2 sides rather than the four
    Sounds like an air flow problem to me.

  5. #5
    Join Date
    Mar 2006
    Location
    belfast
    Posts
    239
    Rep Power
    19

    Re: air well ac

    no deffo not air flow. the coil is clear and plenty of air comming through it

  6. #6
    Join Date
    Feb 2007
    Location
    UK
    Posts
    2,473
    Rep Power
    45

    Re: air well ac

    I know that Airwell used to have some strange coil arrangements.
    Is it one continuos coil that's been bent around (as in a Daikin or Toshiba for example) or is there 4 individual coils?

    Is it two sides 90 degrees to each-other that cools or are they opposite each-other?

  7. #7
    Join Date
    Mar 2006
    Location
    belfast
    Posts
    239
    Rep Power
    19

    Re: air well ac

    to be totally honest i dont no about the coil shape because i havent had the fascia off.

    its the closest to the inlet pipes that are cooling

    so you have the first side cooling then 90 to that the next kinda cools then 90 and 90 again arent
    Last edited by thebigcheese; 28-06-2009 at 05:08 PM.

  8. #8
    Join Date
    Feb 2007
    Location
    UK
    Posts
    2,473
    Rep Power
    45

    Re: air well ac

    i havent had the fascia off
    So how do you know that the coil is clear???

  9. #9
    Join Date
    Mar 2006
    Location
    Lancashire
    Posts
    1,859
    Rep Power
    28

    Re: air well ac

    Quote Originally Posted by thebigcheese View Post
    to be totally honest i dont no about the coil shape because i havent had the fascia off.

    its the closest to the inlet pipes that are cooling

    so you have the first side cooling then 90 to that the next kinda cools then 90 and 90 again arent
    I would strip the indoor unit down to have a closer inspection at the coil. By doing this you can usually tell what the problem is, wether it be a faulty LEV, dirty coil or blockage in the suction.

    I had a fault like this a few months back and it turned out to be a partial blockage on the strainer in the evap outlet. Did you also check the evap outlet?
    The difference between genius and stupidity is that genius has its limits.

    Marc

  10. #10
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: air well ac

    Quote Originally Posted by thebigcheese View Post
    no deffo not air flow. the coil is clear and plenty of air comming through it
    Yes... it is definitely an airflow problem.

  11. #11
    Join Date
    Mar 2006
    Location
    belfast
    Posts
    239
    Rep Power
    19

    Re: air well ac

    i have had the filter section out and check the coil from here which is spotless, the airflow from the unit is great and can be felt from ground level.

    as for the strainer i am only aware of there being 1 as this is fitted during installation

  12. #12
    Join Date
    Mar 2006
    Location
    Lancashire
    Posts
    1,859
    Rep Power
    28

    Re: air well ac

    On some type of casettes they have mesh strainers inside the flare nuts to stop stuff getting in the coil.
    The difference between genius and stupidity is that genius has its limits.

    Marc

  13. #13
    Join Date
    Mar 2006
    Location
    belfast
    Posts
    239
    Rep Power
    19

    Re: air well ac

    yea thats wat this is like only it has a flare conection on one end a flare nut on the other but its clear

  14. #14
    Join Date
    Feb 2007
    Location
    UK
    Posts
    2,473
    Rep Power
    45

    Re: air well ac

    Depending on how the maintenance been done...

    We took a sit over last year where several units had these type of problem.
    The coils looked spotless until the fascias and drip-trays came off, the previous mob had clearly brushed the inside face of the coil but they were blocked solid between the fins. Some of the units even had plants growing in their drip-trays.
    None of which could be spotted with the fascias still on.
    (That was in an area where they had some 4 metric tonnes of paper going through each day, 7 days a week)

  15. #15
    Join Date
    Mar 2006
    Location
    belfast
    Posts
    239
    Rep Power
    19

    Re: air well ac

    i honestly dont think its an airflow problem but i will drop the fascia tomorrow to be 100% sure

  16. #16
    Join Date
    Mar 2006
    Location
    belfast
    Posts
    239
    Rep Power
    19

    Re: air well ac

    all sorted went to move a bottle of 407c in the van and thought thats very light for a new bottle. turns out it was leaking........ recovered full charge from system vaced out and charged with a diff bottle hey presto

    thanks for the help anyhow