Thread: Daikin Leak
27-06-2009, 09:46 PM #1
Daikin Leak
Found a leak on Friday on A Daikin 3 pipe outdoor. Model number of the unit is a REYQ8m7w1B. What is the procedure to make sure all the valves are open when reclaiming the remainder of the gas so I get all the gas out?
27-06-2009, 11:02 PM #2
Re: Daikin Leak
Leak on the condensor on just on the system?
27-06-2009, 11:20 PM #3
Re: Daikin Leak
Leak on the condensor. One of the small pipes inside the unit.
27-06-2009, 11:58 PM #4
Re: Daikin Leak
i think you can do a master reset which will drive all the valves open, i know it works on all bs box and fan coils but not sure about condensing unit, i cant remember exactly how but its done via the push switch buttons on o/d main pcb
29-06-2009, 09:46 PM #5
Re: Daikin Leak
Thanks for the help hopefully I will find something.
30-06-2009, 12:32 AM #6
Re: Daikin Leak
You need to set mode 2 setting 21 on the outdoor PCB, this will open SV's and expansion valves to allow correct vac, pressure test etc. Dont suppose the leak was at a small capillary line just off the oil seperator?
04-07-2009, 04:06 PM #7
Re: Daikin Leak
Thanks for the info. I was not aware of the setting but I managed to reclaim all of the gas. It was a fluke finding the leak the lad that I was with spotted a small trace of oil on a pipe sprayed some bubbles on it and there she was.The leak was on a small 3/8 pipe on the liquid side.
Mitsubishi Gas leak? PURY P250 YGMA
By marc5180 in forum Air ConditioningReplies: 82Last Post: 31-12-2010, 07:28 PM -
USX Ultrasonic Leak Detector advice
By rick19821982 in forum Tools and CalculatorsReplies: 3Last Post: 24-06-2009, 08:43 PM -
Fixing Daikin A3 Error
By Stuffy in forum Air ConditioningReplies: 3Last Post: 27-03-2009, 06:02 AM -
Leak Testing Daikin K Series VRV
By jedi in forum Trouble ShootingReplies: 8Last Post: 21-08-2008, 07:16 PM -
Evasive gas leak
By Feeze in forum Technical DiscussionsReplies: 24Last Post: 18-08-2008, 07:22 AM