    Daikin Leak



    Found a leak on Friday on A Daikin 3 pipe outdoor. Model number of the unit is a REYQ8m7w1B. What is the procedure to make sure all the valves are open when reclaiming the remainder of the gas so I get all the gas out?



  2. #2
    Join Date
    Jun 2009
    Location
    East Anglia
    Age
    38
    Posts
    204
    Rep Power
    15

    Re: Daikin Leak

    Leak on the condensor on just on the system?

  3. #3
    Join Date
    Nov 2008
    Location
    Ireland
    Posts
    55
    Rep Power
    16

    Re: Daikin Leak

    Leak on the condensor. One of the small pipes inside the unit.

  4. #4
    Join Date
    Nov 2006
    Location
    At home
    Posts
    181
    Rep Power
    18

    Re: Daikin Leak

    i think you can do a master reset which will drive all the valves open, i know it works on all bs box and fan coils but not sure about condensing unit, i cant remember exactly how but its done via the push switch buttons on o/d main pcb

  5. #5
    Join Date
    Nov 2008
    Location
    Ireland
    Posts
    55
    Rep Power
    16

    Re: Daikin Leak

    Thanks for the help hopefully I will find something.

  6. #6
    Join Date
    Mar 2006
    Location
    Glasgow, Scotland
    Posts
    177
    Rep Power
    19

    Re: Daikin Leak

    You need to set mode 2 setting 21 on the outdoor PCB, this will open SV's and expansion valves to allow correct vac, pressure test etc. Dont suppose the leak was at a small capillary line just off the oil seperator?

  7. #7
    Join Date
    Nov 2008
    Location
    Ireland
    Posts
    55
    Rep Power
    16

    Re: Daikin Leak

    Thanks for the info. I was not aware of the setting but I managed to reclaim all of the gas. It was a fluke finding the leak the lad that I was with spotted a small trace of oil on a pipe sprayed some bubbles on it and there she was.The leak was on a small 3/8 pipe on the liquid side.

Similar Threads

  1. Mitsubishi Gas leak? PURY P250 YGMA
    By marc5180 in forum Air Conditioning
    Replies: 82
    Last Post: 31-12-2010, 07:28 PM
  2. USX Ultrasonic Leak Detector advice
    By rick19821982 in forum Tools and Calculators
    Replies: 3
    Last Post: 24-06-2009, 08:43 PM
  3. Fixing Daikin A3 Error
    By Stuffy in forum Air Conditioning
    Replies: 3
    Last Post: 27-03-2009, 06:02 AM
  4. Leak Testing Daikin K Series VRV
    By jedi in forum Trouble Shooting
    Replies: 8
    Last Post: 21-08-2008, 07:16 PM
  5. Evasive gas leak
    By Feeze in forum Technical Discussions
    Replies: 24
    Last Post: 18-08-2008, 07:22 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •