    Piping layout question



    I have recently started to commissioning some refrigeration equipment (mainly flake ice makers, ice water and and coolers for fishing boats) and contractor, I work for, telling me that I should make pipe arrangement as at #1 at following picture.




    My current practice was #2 when there is no pump down or #3 when there is pump down. Both cases are when condenser (and compressor) are below evaporator.

    It is interesting that is said to me that #1 is for R404A refrigerant and that blind pipe piece after T must bee 10" (25 cm) long. Also there is no need for oil trap in this case.
    Since I cannot find any reference at that pipe arrangement in any literature, could someone comment on theory behind this and is this good practice and/or to point me to literature where this case is explained?
    Last edited by nike123; 27-06-2009 at 05:33 PM.



  2. #2
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: Piping layout question

    #2 and #3 are obvious to me.

    #1 is something new, interesting idea. I'm sure that there is some logic behind it.
    Maybe Us iceman or Gary will shed some light on it.

  3. #3
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Piping layout question

    Quote Originally Posted by chemi-cool View Post
    #2 and #3 are obvious to me.

    #1 is something new, interesting idea. I'm sure that there is some logic behind it.
    Maybe Us iceman or Gary will shed some light on it.
    Yes, it is new. They said that some Italian engineer has advised that to them few years ago, and they, since then, always fit pipes in that manner. I am not sure if the same case is even with pump down.
    They said also that oil return problem is not existent since introduction of that piping practice.
    It is pointed to me that for R404A is very important that blind pipe is very close to 10".

  4. #4
    Join Date
    Apr 2008
    Location
    canada
    Age
    75
    Posts
    94
    Rep Power
    17

    Re: Piping layout question

    They said also that oil return problem is not existent since introduction of that piping practice.
    It is pointed to me that for R404A is very important that blind pipe is very close to 10".[/quote]


    B”Hfficeffice" />>>

    Do you mean that was a problem with oil return with P-trap enragement and by switching to the new arrangement the problem disappeared? >>

  5. #5
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    37

    Re: Piping layout question

    Hi Nike123,
    I haven't heard about this new concept either.
    But thinking about it, with 404A system with good oil separation that the system will be oil free, and with out pumpdown, liquid carry from evaps will be assisted by traps, but with dead end extention would stop carryover to compressor and effectively store and allow to boil off at evaporator.
    I would be inclined to fit a schrader on bottom of extension for future oil draining if necessary.
    I could be completely wrong though.
    magoo
    Last edited by Magoo; 02-07-2009 at 02:00 AM.

  6. #6
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Piping layout question

    Quote Originally Posted by michaelm View Post



    Do you mean that was a problem with oil return with P-trap enragement and by switching to the new arrangement the problem disappeared?
    n Yes. That is also how I understood them.

  7. #7
    Join Date
    Jun 2007
    Location
    South Africa
    Age
    66
    Posts
    120
    Rep Power
    17

    Re: Piping layout question

    No.1 looks like somebody could not decide where to go from there. Have never seen something like this.

  8. #8
    Join Date
    May 2006
    Location
    India
    Age
    74
    Posts
    399
    Rep Power
    18

    Re: Piping layout question

    #1 arrangement will need the verticle pipe entering horizontal pipe carry upto the bottom ( 1 or 2 mm ) above of the horizontal suction pipe. Besides, the verticle pipe will need a 45 degrees cut . the cut section of pipe will face the gas flow out of evaporator ; which will pick up any residual oil if any alongwith refrigerant.

  9. #9
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Piping layout question

    Quote Originally Posted by D.D.KORANNE View Post
    #1 arrangement will need the verticle pipe entering horizontal pipe carry upto the bottom ( 1 or 2 mm ) above of the horizontal suction pipe. Besides, the verticle pipe will need a 45 degrees cut . the cut section of pipe will face the gas flow out of evaporator ; which will pick up any residual oil if any alongwith refrigerant.

    It seems that you are familiar with that arrangement. Do you maybe have any reference in book or some article about that?

Similar Threads

  1. Layman question re R410 tubing (xposting from Refrigerants)
    By greekguy in forum Air Conditioning
    Replies: 6
    Last Post: 21-12-2010, 09:25 PM
  2. Replies: 1
    Last Post: 02-06-2009, 04:01 PM
  3. Refriferation cycle question
    By ozmecheng in forum Fundamentals
    Replies: 32
    Last Post: 26-03-2008, 10:38 PM
  4. Customer question re Daikin piping
    By thegeby in forum Air Conditioning
    Replies: 2
    Last Post: 17-01-2008, 09:57 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •