    Psychrometric question



    Senerio ---- 100% outside air unit moving 2000 cfm with an outside air temperatureof 30 degrees F.
    How many watts of electric heat will it take to raise the supply air temperature to 70 degrees F ?

    Altitude = sea level
    specific density = .075 lb/cubic foot

    The answer i came up with just doesn't look right, need to see someone elses calculcations.

    thanks



  2. #2
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Psychrometric question

    30F = 1.1111C
    70F = 21.1111C

    therefore dt = 20C

    1CFM = 0.028317m3/s therefore 2000CFM = 56.634m3/s

    56.634m3/s x 20C = 1381.86kW

    It's a little difficult when you mix SI units with Imperial units in your question.

  3. #3
    crusty demon's Avatar
    crusty demon Guest

    Re: Psychrometric question

    86,400 btu
    25,307.55 watts
    25.3 kw
    is this correct?

  4. #4
    Join Date
    Jun 2006
    Location
    British West Indies
    Posts
    543
    Rep Power
    18

    Re: Psychrometric question

    2000/12.4x60x(19.81-10.16)/3413= 27.4 kW

    30 degree air is a little denser, probably some water vapour in it as well

    end up with more than 2000 CFM of supply
    Take the V out of HVAC and you are left with a HAC job

  5. #5
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Psychrometric question

    Quote Originally Posted by frank View Post

    1CFM = 0.028317m3/s therefore 2000CFM = 56.634m3/s
    1cfm = 0.0004719 m3/s

    2000CFM = 0.9438948864 m3/s

    Required heat is: 24,5 kW

    Last edited by nike123; 27-06-2009 at 06:40 PM.

  6. #6
    Join Date
    Jun 2006
    Location
    British West Indies
    Posts
    543
    Rep Power
    18

    Re: Psychrometric question

    2000 / 60 x .3048^3 = 0.9438948...... cubic meters per second

    30F is -1.11111C, its below freezing

    24.49 x 22.1/20= 27.06 Kw

    I allowed for about 80% RH to get 27.4
    Take the V out of HVAC and you are left with a HAC job

  7. #7
    Join Date
    Jun 2006
    Location
    British West Indies
    Posts
    543
    Rep Power
    18

    Re: Psychrometric question

    the answer depends on whether you measure the cold air or the heated air flow
    Take the V out of HVAC and you are left with a HAC job

  8. #8
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Psychrometric question

    Quote Originally Posted by Abby Normal View Post

    30F is -1.11111C, its below freezing

    It seems that Frank has got hard Saturday.

    30F = 1.1111C


    1CFM = 0.028317m3/s therefore 2000CFM = 56.634m3/s

  9. #9
    Join Date
    Jun 2006
    Location
    British West Indies
    Posts
    543
    Rep Power
    18

    Re: Psychrometric question

    NASA crashed 9 figures worth of probes into Mars because they had problems with IP and metric
    Take the V out of HVAC and you are left with a HAC job

  10. #10
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Psychrometric question

    I know, I know. I saw it and then realised that you would all start pulling my leg before too long

    Note to self. DON'T do calc's after BEER!

  11. #11
    Join Date
    Feb 2006
    Location
    Mumbai
    Posts
    49
    Rep Power
    0

    Re: Psychrometric question

    Sensible Heat (Btu/hr) = 1.08 x cfm x (Delta T)
    =1.08 x 2000 x (70 - 30)
    =86400 Btu/hr
    =25Kw.
    Vijay Kumar
    HVAC Design Engineer

    BMCPL

    "The more you sweat in peace less you bleed in war"

Similar Threads

  1. Replies: 1
    Last Post: 02-06-2009, 04:01 PM
  2. Heat Transfer Exam Question
    By alexdouglas1969 in forum Fundamentals
    Replies: 10
    Last Post: 13-12-2008, 04:19 PM
  3. Refriferation cycle question
    By ozmecheng in forum Fundamentals
    Replies: 32
    Last Post: 26-03-2008, 10:38 PM
  4. quizy type question thingy
    By rbartlett in forum Chit Chat & Service Stories
    Replies: 25
    Last Post: 06-02-2006, 09:22 PM
  5. Urgent, Kirchoff question
    By Peter_1 in forum Fundamentals
    Replies: 4
    Last Post: 20-01-2004, 03:12 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •