26-06-2009, 09:31 PM #1
Super heat
I was wondering if someone could help , what is the best way to check my super heat on a diary cabinet? were would be the best places to put my temp probes T1 and T2 to check to c if the superheat is ok on the system and would around 6 C be ok for the difference in the 2 probes for superheat with R 404a. Cheers
Last edited by Peter_1; 28-06-2009 at 08:05 AM.
-
26-06-2009, 09:40 PM #2
Re: Super heat
Gauges: attach to suction, note the Saturation temperature.
Temp probe: ideally attach 'tightly' to suction as close to the TEV phial as poss, note the temperature.
Difference between saturation temp and actual pipe
temp is your superheat, ideally 6C
You could attach your temp probe further away from TEV phial if its more convenient but the results won't be as accurate.
-
27-06-2009, 05:37 PM #3
Re: Super heat
Allow the system to operate for 20 - 30 minutes to stabilize. Connect gauges that is accurate to suction side of system. Read pressure and convert to temperature, reading a PT chart. Connect a good thermometer to the suction line near the sensing bulb of the TXV valve. Record the suction line temperature.
Subtract the saturated temperature from the actual suction line temperature. Result is the operating superheat.
Example: Suction line temp. = 55F
Suction pressure = 68.5 psig
68.5 psig = 40F
55 - 40F = 15 F Superheat.
Hope this helps
-
27-06-2009, 05:51 PM #4
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
Re: Super heat
That depend on what superheat you want to measure.
- If you want to measure evaporator superheat, best place is around TXV phial, if it is TXV metering device and at around 20-30 cm after evaporator if it is capillary/orifice metering device.
- If you want to measure total superheat, best is around 20-30 cm before compressor.
- If you want to measure discharge superheat than best is 20-30 cm after compressor.
-
28-06-2009, 08:08 AM #5
-
29-06-2009, 01:24 AM #6
-
21-07-2009, 01:06 PM #7
Re: Super heat
cheers for the help
Similar Threads
-
Capacity control
By sparrow in forum TrainingReplies: 44Last Post: 18-01-2010, 07:49 PM -
Some information on the aplication of suction gas/liquid line heat exchangers
By SteinarN in forum FundamentalsReplies: 5Last Post: 14-09-2009, 07:33 AM -
seting super heat
By citytosurf in forum CommercialReplies: 21Last Post: 05-02-2009, 03:14 AM -
frostles heat pump
By Lc_shi in forum New TechnologiesReplies: 27Last Post: 31-03-2008, 07:53 AM -
Help pls: air-to-air heat exchanger and Regenerative heat exchanger?
By spiderman in forum New TechnologiesReplies: 10Last Post: 18-07-2007, 08:07 AM