    Re: Vilter tuning/unload and load setpoints

    squidward ,
    When you say hot gas bypass do you mean high pressure gas from liquid reciever into compressor suction line ?

    If so you could also use a regulating valve ( crankcase pressure regulator ) .
    On low loads it will modulate high pressure gas into suction line to keep pressures more smooth and constant .

    The solonoid can be used as a back up with pressure switch in case modulating valve leaks etc .
    If liquid level in evap not high enough or reciever level low ( blowing hp gas into evap ) suction pressures will also fluctuate wildly . Normally liq reciever level should be high enough to allow for varying loads , condensor fan cycling etc .

    Looks like your on the right track anyway .
    Last edited by RANGER1; 27-06-2009 at 10:32 PM. Reason: paragraph spacing

Similar Threads

  1. Sensible Heat Factor / capacity of Inverter split Systems at part load?
    By Greengrocer in forum Technical Speculations
    Replies: 31
    Last Post: 09-02-2009, 04:57 PM
  2. Heat transfer coefficient - Coolpack
    By Graham in forum Fundamentals
    Replies: 10
    Last Post: 28-05-2008, 01:08 AM
  3. Compressor loading, cooling, and range of operation.
    By Air duster in forum Fundamentals
    Replies: 10
    Last Post: 02-04-2008, 08:39 AM
  4. How is load divided between indoor units
    By mchild in forum Air Conditioning
    Replies: 26
    Last Post: 17-01-2008, 10:30 PM
  5. AKV versus higher load
    By Peter_1 in forum Industrial
    Replies: 20
    Last Post: 18-04-2004, 11:05 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •