26-06-2009, 07:16 PM #1
converting from r12
just been to my dads pub as he has a walk in fridge in the cellar that was not working. After diagnosing it has having no gas i then leak checked the unit and repaired the leak but found it to be running on r12. should i chrge unit with r134a and will i have to change the expansion valve as it is a danfoss tx2 r12. not up on these fridges as i normally work on trasport stuff. your help would be much appreciated cheers eddie
-
26-06-2009, 07:36 PM #2
Re: converting from r12
You can get R409a as a drop in replacement for R12 with no changes. A long term soloution would be R134a but yes you would have to change the TEV and also change the oil and flush the system. Hope this helps
-
26-06-2009, 09:10 PM #3
Re: converting from r12
you could try r413a, make sure you change the drier. hope this helps, make sure you vac out before charging
-
26-06-2009, 11:33 PM #4
Re: converting from r12
I tend to use R413A as well, or sometimes called isceon 49.
works good as a drop in, might have to adjust the superheat a bit, generally charge 10% less than recommended charge and expect flashing in the sight glass.
-
01-07-2009, 12:46 PM #5
Re: converting from r12
best choice is the long term retrofit with r134a and poe oil but this takes time and about 3-4 oil changes to get less than 5% mineral oil in the mix also have to change expantion device and dryer
-
02-07-2009, 05:55 AM #6
Re: converting from r12
I have converted many systems from r-12 to 134a, as mentioned above you must change the oil to POE, and change the oil at least 4 to 5 times to get the mineral oil down below the 5 % mark, a refractometer is good for this, it will tell you when your safe , change your driers, POE will break loose particles in the system, as far as your TXV, leave it alone, the same txv will work with the 134a , do check your txv for a removable inlet screen, if so, clean it after system runs a few days, set your super heat
Similar Threads
-
Converting a Freezer to a Curing Box
By robbo in forum DomesticReplies: 17Last Post: 28-05-2011, 03:21 PM -
converting a calculation to Si
By marc5180 in forum FundamentalsReplies: 14Last Post: 10-05-2009, 09:41 PM -
converting refrigerant volume to mass
By tiggla01 in forum Tools and CalculatorsReplies: 2Last Post: 06-06-2008, 02:06 PM -
Converting an ac to a heatpump
By modengineer in forum FundamentalsReplies: 5Last Post: 10-03-2007, 09:05 PM -
Converting Care back to HCFC's
By Latte in forum RefrigerantsReplies: 4Last Post: 25-10-2004, 10:10 PM