    converting from r12



    just been to my dads pub as he has a walk in fridge in the cellar that was not working. After diagnosing it has having no gas i then leak checked the unit and repaired the leak but found it to be running on r12. should i chrge unit with r134a and will i have to change the expansion valve as it is a danfoss tx2 r12. not up on these fridges as i normally work on trasport stuff. your help would be much appreciated cheers eddie



  2. #2
    Join Date
    Mar 2008
    Location
    United Kingdom
    Posts
    52
    Rep Power
    17

    Re: converting from r12

    You can get R409a as a drop in replacement for R12 with no changes. A long term soloution would be R134a but yes you would have to change the TEV and also change the oil and flush the system. Hope this helps

  3. #3
    Join Date
    Jun 2008
    Location
    gloucester
    Age
    44
    Posts
    72
    Rep Power
    16

    Re: converting from r12

    you could try r413a, make sure you change the drier. hope this helps, make sure you vac out before charging

  4. #4
    Join Date
    Dec 2004
    Location
    U.K
    Age
    55
    Posts
    518
    Rep Power
    21

    Re: converting from r12

    I tend to use R413A as well, or sometimes called isceon 49.

    works good as a drop in, might have to adjust the superheat a bit, generally charge 10% less than recommended charge and expect flashing in the sight glass.

  5. #5
    hot chilly's Avatar
    hot chilly Guest

    Re: converting from r12

    best choice is the long term retrofit with r134a and poe oil but this takes time and about 3-4 oil changes to get less than 5% mineral oil in the mix also have to change expantion device and dryer

  6. #6
    Dieppert's Avatar
    Dieppert Guest

    Re: converting from r12

    I have converted many systems from r-12 to 134a, as mentioned above you must change the oil to POE, and change the oil at least 4 to 5 times to get the mineral oil down below the 5 % mark, a refractometer is good for this, it will tell you when your safe , change your driers, POE will break loose particles in the system, as far as your TXV, leave it alone, the same txv will work with the 134a , do check your txv for a removable inlet screen, if so, clean it after system runs a few days, set your super heat

Similar Threads

  1. Converting a Freezer to a Curing Box
    By robbo in forum Domestic
    Replies: 17
    Last Post: 28-05-2011, 03:21 PM
  2. converting a calculation to Si
    By marc5180 in forum Fundamentals
    Replies: 14
    Last Post: 10-05-2009, 09:41 PM
  3. converting refrigerant volume to mass
    By tiggla01 in forum Tools and Calculators
    Replies: 2
    Last Post: 06-06-2008, 02:06 PM
  4. Converting an ac to a heatpump
    By modengineer in forum Fundamentals
    Replies: 5
    Last Post: 10-03-2007, 10:05 PM
  5. Converting Care back to HCFC's
    By Latte in forum Refrigerants
    Replies: 4
    Last Post: 25-10-2004, 10:10 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •