    Unhappy Reefer container issue - need assist



    Hi all, just need your assistance. as i've a case that shipper get un professional technician and played with the reefer equipment of the carrier. after my reefer contractor checked the container he advised below. so can anybody advise if below is true and could be done

    ============quote================
    We found that the customer has actually played with the unit’s control wiring which has resulted by having the evaporator motors rotating in the wrong direction, we have repaired the wiring and the evaporator motors has returned to their normal rotating direction!

    The negative results which we may have resulted if the container is kept by the wrong wiring: having the supply air going UP instead of DOWN and accordingly the supply air sensor will be reading the return air temperature and the return sensor will be reading the supply temperature, and cargo will never reach the setpoint!!!

    On the display you will see that the unit is inrange and achieving the setpoint and everything is normal, but actually this is a fake readings resulting from having the motors rotating in the reverse direction..

    It’s totally not recommended to let the customers play with our reefers..

    ===========unquote========================



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Reefer container issue - need assist

    Seems reasonable but what is it that you want us to say, your contractor has said it all, or am I missing something?
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: Reefer container issue - need assist

    If the fans are three phase then they could easily be made to run backwards, if they are single phase then its still possible to do (and i have seen it done with both three phase and single phase fans on condensers).
    What your contractor said sounds technically feasible, but i don't work on containers so can't say for sure.

  4. #4
    Join Date
    Dec 2004
    Location
    U.K
    Age
    55
    Posts
    518
    Rep Power
    21

    Re: Reefer container issue - need assist

    Yes it could be done, but cannot explain why it would be done.

    I would guess a more likely explanation is that the unit was running backwards via the 3 phase supply.

    This is a simple check that needs to be made when first connecting the unit to mains supply.

    The condenser fan should blow air outwards, the evaporator fans should draw air from the top and blow down through the floor outlets.

Similar Threads

  1. Replies: 12
    Last Post: 27-03-2011, 04:12 AM
  2. Dual Usage of reefer container
    By AsgharMalik in forum Fundamentals
    Replies: 1
    Last Post: 12-04-2010, 10:13 AM
  3. Replies: 1
    Last Post: 01-07-2009, 10:33 AM
  4. Reefer container
    By stevec in forum Commercial
    Replies: 2
    Last Post: 25-01-2009, 05:30 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •