Thread: Pressure-relief valve
13-07-2004, 06:45 PM #1
ANSI / ASHRAE standard 15 (2001) defines a pressure vessel as "any refrigerant-containing receptacle in a refrigeration system" but continues by excluding, for example, evaporator coils and condenser coils from clasification as pressure vessels.
Also, any pressure vessel that contains liquid refrigerant that may be isolated by stop valves located anywhere in the system must be fitted with appropriately sixed overpressure protection?
So, must an evaporative condenser have a pressure relief valve, and must an evaporator (hot gas defrost - not electrical) have a pressure relief valve?
Saludos,
Jan
13-07-2004, 08:23 PM #2
Re: Pressure-relief valve
Hi Jan
It looks like the answer is in the question "that may be isolated by stop valves located anywhere in the system must be fitted with appropriately sixed overpressure protection"
If you have stop valves that isolate the evaporator or condenser then the answer will be yes according to ASHRAE .
Chemi
14-07-2004, 05:57 PM #3
Hi Chemi!
Indeed, when you can trap liquid in a refrigeration system or if the pressure can rise above the design pressure (heating coil etc) you must have a relief device (according to standard 15).
Anyway, if a condenser (coil) is not classified as a pressure vessel, which always need a relief valve, then maybe it does not need any relief valve, as you not likely will fill it with liquid.
Saludos,
Jan
18-07-2004, 03:00 AM #4
Hi Jan,
In a evaporator with hot gas defrost we usually have a pressure regulator valve to keep the pressure inside the coil during the defrost, so in my opinion, this valve works like a pressure relief valve.
Best regards.
Volnei
19-07-2004, 01:14 AM #5
Hi Volnei,
Hot gas defrost could also be working with a HP float valve.
Anyway, if the hot gas pressure regulating valve should count as a pressure relief valve, then you can not have stop valves before or after.
Best regards,
Jan
Building a wine cabinet
By Rory in forum Technical DiscussionsReplies: 38Last Post: 13-07-2004, 08:28 PM -
Relief Valve on Suction
By Latte in forum CommercialReplies: 19Last Post: 20-01-2004, 11:57 PM -
over-under pressure relief valve
By philip de moor in forum IndustrialReplies: 3Last Post: 08-01-2004, 12:50 PM -
Pressure relief valve
By DaBit in forum FundamentalsReplies: 18Last Post: 16-08-2003, 03:11 PM