Results 1 to 12 of 12
Thread: Frick screw compressor
24-06-2009, 01:58 PM #1
I am looking for all the NH3 pro's to help me out. I have a frick RWBII-177H screw compressor I am trying to find out what my oil pressure should be above discharge pressure. The technical specs that came with the compressor list 45-55 psi above suction pressure but that is for a non continuous oil pump. The oil pump on it is designed to run continuosly.
24-06-2009, 06:26 PM #2
Re: Frick screw compressor
According to the Installation-Operation-Maintenance for RWB II models 60-856 the oil pressure should be 20-25 psi (high stage) 30-35 psi (booster) at the highest normal head pressure or intermediate pressure expected with the compressor fully loaded. The compressor will require maximum oil flow under these conditions. This is different for cycling oil pumps, discharge pressure 55 psi above suction, when it falls below 45 psi the pump will start back up.
24-06-2009, 06:37 PM #3
Thanks alot.. I am very glad I found this web site it is a great resource to have people availiable with so much knowledge and experience.
24-06-2009, 06:40 PM #4
I have the manual if you want me to email it to you? Send me a pm and Ill email it to you.
24-06-2009, 06:42 PM #5
I found your email, how long have you been with Perdue?
24-06-2009, 08:07 PM #6
pedersrg,
Have you ever been to the Design of Ammonia Refrigeration Systems class at UW-Madison?If all else fails, ask for help.
06-10-2010, 07:30 AM #7
Sir can i have a copy of frick manuals rwb and rdb. This is my email t0nz04_mendoza@yahoo.com
26-06-2011, 06:27 AM #8
Sir, Please send a copy of the Frick compressor RWB & RDB to mail address
kartheekus@yahoo.com
12-11-2011, 10:23 AM #9
NH3wizard,
Could I also get a copy of the Frick RWB manual at troach@lambgroupllc.com
18-11-2011, 07:29 AM #10
Nice post thanks for sharing.
15-01-2012, 05:56 AM #11
Hi wouldn't mind a copy of the manual myself Model RWBII177e Thanks Steve
15-01-2012, 06:00 AM #12
The email address is steve@freezergeezer.co.nz for the RWBII 177E Manual thanks Steve
Frick screw compressor SGC3515 overhaul manual
By cjlee74 in forum IndustrialReplies: 10Last Post: 13-10-2010, 08:49 AM -
problem with volume on frick screw compressor
By samlee12 in forum IndustrialReplies: 4Last Post: 29-10-2009, 06:06 AM -
Oil Lifting Problem in NH3 screw compressor
By SURESH YADAV in forum Refrigeration - The StoriesReplies: 20Last Post: 16-10-2009, 01:34 AM -
problem with frick screw volume
By samlee12 in forum Industrial CompressorsReplies: 9Last Post: 20-06-2009, 02:46 PM -
parallel operation of screw compressor and piston type
By cheikh ahmed in forum FundamentalsReplies: 9Last Post: 26-08-2008, 08:34 AM