Thread: Remote condenser
-
24-06-2009, 10:05 AM #1
Remote condenser
I am looking into re locating a copeland mc-r7-zf33ke condensing unit. Because of its current position this will be very difficult.
It would be much easier to remove and re install the condenser remotly.
What things should i consider when doing this?
The pipe run is 10m at the moment but the condenser will be a further 10m awy with a 3m rise.
-
24-06-2009, 10:11 AM #2
Re: Remote condenser
Hi,
I do change the location of the condenser before but not that far, i think you have to check the pipe size first, second the oil traps, and you have to fix very well the condenser in the new posiiton
-
24-06-2009, 12:19 PM #3
Re: Remote condenser
Receiver warm up in plant room could make it difficult for liquid drain to receiver , a vent line from receiver to condenser would be of help .