    Remote condenser



    I am looking into re locating a copeland mc-r7-zf33ke condensing unit. Because of its current position this will be very difficult.

    It would be much easier to remove and re install the condenser remotly.

    What things should i consider when doing this?

    The pipe run is 10m at the moment but the condenser will be a further 10m awy with a 3m rise.



  2. #2
    Join Date
    Feb 2008
    Location
    Saudi Arabia
    Age
    52
    Posts
    69
    Rep Power
    17

    Re: Remote condenser

    Hi,

    I do change the location of the condenser before but not that far, i think you have to check the pipe size first, second the oil traps, and you have to fix very well the condenser in the new posiiton

  3. #3
    Join Date
    May 2006
    Location
    India
    Age
    74
    Posts
    399
    Rep Power
    18

    Re: Remote condenser

    Receiver warm up in plant room could make it difficult for liquid drain to receiver , a vent line from receiver to condenser would be of help .

Similar Threads

  1. carrier splt sometimes doesn't respond to remote.
    By paul_h in forum Air Conditioning
    Replies: 10
    Last Post: 14-02-2009, 05:44 AM
  2. Air Cooled Condenser Leakage Problem with R-404A
    By RADHAKRISHNARAO in forum Technical Discussions
    Replies: 19
    Last Post: 30-07-2008, 12:21 PM
  3. Manitowoc remote condenser install
    By hysiderafter in forum Commercial
    Replies: 0
    Last Post: 22-07-2008, 06:43 PM
  4. Remote condenser + heat recovery
    By Renato RR in forum Technical Speculations
    Replies: 9
    Last Post: 30-03-2006, 07:26 AM
  5. Remote condenser
    By Rfcont in forum Technical Discussions
    Replies: 7
    Last Post: 06-12-2005, 12:44 PM

Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •