    Toshiba split



    I am installing two Toshiba under ceiling split casettes in the same room and am wondering how to run both casettes off one controller, Is it as easy as daisy chaining the two casettes on the two core controller cable.I can only find how to run two casettes and one controller if they have the same condenser.
    Last edited by sexysouthwest; 16-06-2009 at 06:08 PM.



  2. #2
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Toshiba split

    Run a 3 core cable from the controller to the first cassette (A+B+C) then run a 2 core cable between the cassettes (A+B)
    This will make them Master/Slave to the controller although they will both respond to the controller settings as one

    Note. This is based on the old Tosh units that had 3 core connections - haven't fitted any Tosh stuff lately)

  3. #3
    Join Date
    Aug 2004
    Location
    England
    Age
    51
    Posts
    744
    Rep Power
    25

    Re: Toshiba split

    Quote Originally Posted by sexysouthwest View Post
    Is it as easy as daisy chaining the two casettes on the two core controller cable.
    This is exactly it, it is all self addressing as well. They take a few minutes mind to shake hands, up to 10 minutes sometimes.

    Eggs

  4. #4
    Join Date
    Mar 2008
    Location
    honiton
    Age
    48
    Posts
    21
    Rep Power
    0

    Re: Toshiba split

    Thanks for your help i will try this tomorrow.

  5. #5
    Join Date
    Aug 2008
    Location
    Baltics
    Age
    62
    Posts
    786
    Rep Power
    16

    Re: Toshiba split

    Some additional settings are probably needed on PCB. Otherwise instead of handshaking the units might start fighting for a leadership.

  6. #6
    Join Date
    Aug 2004
    Location
    England
    Age
    51
    Posts
    744
    Rep Power
    25

    Re: Toshiba split

    Quote Originally Posted by Yuri B. View Post
    Some additional settings are probably needed on PCB. Otherwise instead of handshaking the units might start fighting for a leadership.
    No, none at all.

    Eggs

  7. #7
    Join Date
    Aug 2008
    Location
    Baltics
    Age
    62
    Posts
    786
    Rep Power
    16

    Re: Toshiba split

    Possible to join only /or more than two (Toshibas)?

  8. #8
    Join Date
    Aug 2004
    Location
    England
    Age
    51
    Posts
    744
    Rep Power
    25

    Re: Toshiba split

    Up to 16 splits is fine and self configuring on the standard controller.

    Shhhh, Toshiba are the trades best kept secret, non of that Mitsubishi MAC31 bullshi7 for a job as simple as this.

    Eggs

  9. #9
    Join Date
    Oct 2006
    Location
    west sussex
    Posts
    5
    Rep Power
    0

    Re: Toshiba split

    Quote Originally Posted by sexysouthwest View Post
    I am installing two Toshiba under ceiling split casettes in the same room and am wondering how to run both casettes off one controller, Is it as easy as daisy chaining the two casettes on the two core controller cable.I can only find how to run two casettes and one controller if they have the same condenser.
    Hi, yes it is easy,the tosh splits uses a two core cable, run a +b on remote to a+b on master unit and the daisy chain to the slave, when powered up the unit will self address, one nice trick on these systems are that you can set the indoor unit to ultra high fan speed for high loads of high cielings, oh and use 2core screened cable if you are running the cable near and power cables, this will stop any (noise) interferance
    hope that helps.

  10. #10
    Join Date
    Oct 2006
    Location
    west sussex
    Posts
    5
    Rep Power
    0

    Re: Toshiba split

    one more thing, as you dealer for the tosg tech hand book, gives you all setting, fault codes, part nos, serial nos etc, etc, you wont whant to fit anything else once you have that, tech back up is brilliant

  11. #11
    Join Date
    May 2006
    Location
    Hayling Island, UK
    Age
    60
    Posts
    143
    Rep Power
    21

    Re: Toshiba split

    Yes it is as easy as daisy chaining the control cables on the A&B connections. There are no dip switches or rotary dials to set up, it's all automatic now.

    BUT not 16 of them in the same group - on the new R410A models it's now 8 indoor units (one master & seven followers).

    A group of 16 was possible on R22 & R407C models.

    Cheers

    Loops

  12. #12
    chill it's Avatar
    chill it Guest

    Re: Toshiba split

    Hi guys , ive just started installing Toshiba as an alternitive, technical back up is second to none, their is always some poor tech bod on the end of their tech line 24/7.
    no other supplier gives that service.
    Toshiba is the way forward. DONT TELL DAIKIN!!!

Similar Threads

  1. Toshiba Digital Inverter range?
    By Slim R410a in forum Air Conditioning
    Replies: 19
    Last Post: 18-10-2010, 02:45 PM
  2. Toshiba multi split runs non-stop
    By expat in forum Air Conditioning
    Replies: 4
    Last Post: 30-10-2008, 09:25 AM
  3. Toshiba split
    By philjd26 in forum Air Conditioning
    Replies: 6
    Last Post: 23-09-2008, 10:53 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •