    is it possible



    on a beer cellar cooling unit- hubbard running on r134a what could cause high suction pressure- 3 bar and high discharge pressure 23 bar with a large superheat.is it possible



  2. #2
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: is it possible

    Dirty condenser, fan not working, high ambient temp, etc.

  3. #3
    Join Date
    Jul 2005
    Location
    luton
    Age
    42
    Posts
    87
    Rep Power
    19

    Re: is it possible

    even if the system has a tev fitted? thought high suction was only with capillary as expansion device ?

  4. #4
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: is it possible

    High suction pressure can happen on either, but is more likely on a TEV system.

  5. #5
    Join Date
    Feb 2008
    Location
    adelaide sth.oz
    Posts
    1,015
    Rep Power
    19

    Re: is it possible

    non condensables,unit undersized also
    mmm to beer or not to beer...........lets drink breakfast

  6. #6
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    37

    Re: is it possible

    All the above, listen to Gary's comments.
    Have you checked compressor motor current?.
    Something will blow soon, nothing surer. R 134A is reasonably tolerant, but compressor, probably not.
    magoo
    magoo

  7. #7
    Join Date
    Feb 2008
    Location
    manchester
    Posts
    80
    Rep Power
    17

    Re: is it possible

    with the hot spell were having at the mo in the uk you can expect that on 134a. the units will struggle on 134a on cellar cooler not the best refrigerant to have a cellar on i perfere 407c or 404a get alot better duty at of it. unfortantly it will take a while for it to pull the cellar down pos 24hrs after repair. as gary says make sure cond clean

  8. #8
    Join Date
    Mar 2008
    Location
    United Kingdom
    Posts
    51
    Rep Power
    17

    Re: is it possible

    I have to agree with lowcool, if your liquid line is cool to cold and it is not unit expansion then you must have air/nitrogen in the system, unless it is severley overcharged, especially if the unit has worked before.
    If it is the case, decant,pressure test,good vac and if it has a charge weight then weigh the gas back in.

  9. #9
    Join Date
    Jul 2005
    Location
    luton
    Age
    42
    Posts
    87
    Rep Power
    19

    Re: is it possible

    thanks went back today used coil cleaner on condenser and blasted with ofn suction went down to 2.2 bar and dicharge to 15 bar liquid line was too hot to touch before at tev but was warm to touch after room temp was 17 celcius and air off evap coil was 14 celcius