    Daikin ERC5CBW1 problem??



    Hey fellas,While carrying out maintenance today i came across this. Unit showing it was running with setpoint set at 16 deg,When i looked at the condensor nothing running? when i opened it up found the unit of on the low pressure switch,i checked the indoor coil which had a bag filter on and slightly dirty i removed it just while i tried to run it up and coil was spotless,Condensor coil a bit of corroding away but nothing to major. I then reset the low pressure switch and after a few seconds it fired up felt the liquid going into the TEV which was warm suction cool and getting colder then it tripped of again??? reset it again and same thing happened ???so i then linked the pressure switch out while i got various temps around the system and pressure's before i left to go home.

    Suction pressure- 5 bar,Touch temp of suction 6 inch away from gauge point was 14 deg C.

    Liquid pressure- 46 bar,Touch temp of liquid 6 inch away from gauge point was 73 deg C.

    Temp going into TEV- 71 deg C.
    Temp out of TEV- 31 deg C.

    Suction straight after evap- 12 deg C.
    Discharge temp- 135 deg C.

    Air on condensor was 22 deg C. Air off was 32 deg C.

    Air on evap was 23 deg C. Air off evap was 22 deg C.

    Daikin-ERC5CBW1 R22 3.5KG YEAR 1995

    just want to see what you fellas think is up with the system as i have had various suggestion's put to me thanks alot

    adam

    p.s was unable to gain discharge pressure due to the schrader being ****y and was firing refrigerant out!


    ajj

  2. #2
    Join Date
    Aug 2008
    Location
    Baltics
    Age
    62
    Posts
    786
    Rep Power
    16

    Re: Daikin ERC5CBW1 problem??

    Hello.
    The air off cond should be much much bigger - +45C maybe at least. It seems the fan is scarcely turning. The relay tripping is probably one combined LP and HP.

  3. #3
    Join Date
    Aug 2008
    Location
    Baltics
    Age
    62
    Posts
    786
    Rep Power
    16

    Re: Daikin ERC5CBW1 problem??

    22C in 32C off seems to be only an illusion that fan runs OK. Is there indeed a rather strong off air flow felt ?

  4. #4
    Join Date
    Aug 2008
    Location
    Baltics
    Age
    62
    Posts
    786
    Rep Power
    16

    Re: Daikin ERC5CBW1 problem??

    Or if the fan OK, then, incondensables - HP heavily increased while temp in the condenser in norm.

  5. #5
    Join Date
    Oct 2008
    Location
    mallorca, spain,
    Age
    75
    Posts
    768
    Rep Power
    19

    Re: Daikin ERC5CBW1 problem??

    you say you could not put your discharge gaugue on cos the schrader is leaking , dont you carry a shrader extraction tool?

  6. #6
    Join Date
    Mar 2006
    Location
    Lancashire
    Posts
    1,859
    Rep Power
    28

    Re: Daikin ERC5CBW1 problem??

    So from discharge line temp to liquid line temp it loses 135ºC-73ºC which is 52ºC but your air condensor off is only 10ºC difference.
    I'd say problem with your fan but can't understand why you would be getting 135ºC at the discharge.

    Could this be a compressor on its way out coupled with the fan not working properly.
    The difference between genius and stupidity is that genius has its limits.

    Marc

  7. #7
    Join Date
    Feb 2007
    Location
    north west
    Age
    36
    Posts
    243
    Rep Power
    18

    Re: Daikin ERC5CBW1 problem??

    Hi Yuri B to be truthful the condensor fan ran but seemed slow then sped up,on a second time of running it it just hummed then, When i gave it a nudge away it went possibly faulty fan or run capacitor i took the amps of the fan and they were at 12amps and dropped to 5amps as it sped up.
    As for the removal took sedgy i do have one but it is not a normal schrader its one of the mushroom type head ones.

    cheers adam
    ajj

  8. #8
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Daikin ERC5CBW1 problem??

    Quote Originally Posted by airconadam View Post
    Hey fellas,While carrying out maintenance today i came across this. Unit showing it was running with setpoint set at 16 deg,When i looked at the condensor nothing running? when i opened it up found the unit of on the low pressure switch,i checked the indoor coil which had a bag filter on and slightly dirty i removed it just while i tried to run it up and coil was spotless,Condensor coil a bit of corroding away but nothing to major. I then reset the low pressure switch and after a few seconds it fired up felt the liquid going into the TEV which was warm suction cool and getting colder then it tripped of again??? reset it again and same thing happened ???so i then linked the pressure switch out while i got various temps around the system and pressure's before i left to go home.

    Suction pressure- 5 bar,Touch temp of suction 6 inch away from gauge point was 14 deg C.

    Liquid pressure- 46 bar,Touch temp of liquid 6 inch away from gauge point was 73 deg C.

    Temp going into TEV- 71 deg C.
    Temp out of TEV- 31 deg C.

    Suction straight after evap- 12 deg C.
    Discharge temp- 135 deg C.

    Air on condensor was 22 deg C. Air off was 32 deg C.

    Air on evap was 23 deg C. Air off evap was 22 deg C.

    Daikin-ERC5CBW1 R22 3.5KG YEAR 1995

    just want to see what you fellas think is up with the system as i have had various suggestion's put to me thanks alot

    adam

    p.s was unable to gain discharge pressure due to the schrader being ****y and was firing refrigerant out!
    You have got to be joking - right?

    Temp into TEV = 71C
    Temp after TEV = 31C
    Temp at Suction just after Evap = 12C???????

    Sounds like the evaporator is acting as a condenser, adding temperature into the space instead of the other way around and condensing vapour, however, the decrease in temperature across the evap (23C-22C) says otherwise.

    First thing I would do is recover, pressure test and recharge, then take another set of readings.

  9. #9
    Join Date
    Feb 2007
    Location
    north west
    Age
    36
    Posts
    243
    Rep Power
    18

    Re: Daikin ERC5CBW1 problem??

    Hey frank i wish i was joking!! I thought this would be a weird one.

    I did check all the reading's 2 or 3 times aswel to make sure.The system seems to contradict itself????? think i may do as you say frank and see were it leads me.Also tho why trip of on low pressure with the pressure at 5bar?????

    There is 2 pressure switches HP and LP

    cheers
    adam
    ajj

  10. #10
    Join Date
    Mar 2006
    Location
    Lancashire
    Posts
    1,859
    Rep Power
    28

    Re: Daikin ERC5CBW1 problem??

    Faulty low pressure switch.
    The difference between genius and stupidity is that genius has its limits.

    Marc

  11. #11
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Daikin ERC5CBW1 problem??

    You keep saying low pressure switch but you are showing a liquid pressure of 46 bar.

    Doesn't that strike you as a tad high ?
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  12. #12
    Join Date
    Feb 2007
    Location
    north west
    Age
    36
    Posts
    243
    Rep Power
    18

    Re: Daikin ERC5CBW1 problem??

    Just a tad Brian just asking why would it go off on low pressure tho!!

    maybe faulty?

    adam
    ajj

  13. #13
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Daikin ERC5CBW1 problem??

    Are you sure that it is the low pressure switch and not the high pressure switch that is tripping? That's why I asked.

    Is it a combined low/high switch unit?
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  14. #14
    Join Date
    Feb 2007
    Location
    north west
    Age
    36
    Posts
    243
    Rep Power
    18

    Re: Daikin ERC5CBW1 problem??

    Ah rite sorry Brian, no there is 2 pressure switches and i only linked out the one being LP. HP switch still connected to the discharge,will try and get the discharge pressure tommorrow thanks alot

    adam
    ajj

Similar Threads

  1. Noise problem on DAIKIN 4MXS68F2
    By cool#9 in forum Air Conditioning
    Replies: 3
    Last Post: 03-01-2009, 02:43 PM
  2. Daikin split problem (any ideas)
    By airconjohn in forum Air Conditioning
    Replies: 14
    Last Post: 17-02-2008, 08:40 PM
  3. Problem with an inverter compressor in V.R.V system DAIKIN R 407
    By Harris Greece in forum Air Conditioning
    Replies: 10
    Last Post: 24-11-2007, 12:53 AM
  4. !!big Daikin Problem!! Codes,u4,pj, And E0
    By airconengineer in forum Air Conditioning
    Replies: 21
    Last Post: 31-05-2007, 09:04 PM
  5. Daikin problem
    By Jambo in forum Trouble Shooting
    Replies: 4
    Last Post: 28-07-2006, 07:42 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •