    Air cooler broken



    Hi,
    I have interesting situation.
    We have installed air cooler of Hans Guentner company , and after few days of operation, customer reported cooler break-down.
    After inspection, we have tried to claim from manufacturer warranty, in order to get the new cooler for replacement.
    We have got the answer that the cooler was broken because of freezing from inside.
    I have reminded them that cooling medium is 30% mixture of ethylene glycol and water, and in the room is +8degC, so there is no way to freeze it from outside.
    The glycol is cooled by ammonia at -8deC, by plate heat exchanger, and glycol temperature is -5/-1degC, so if glycol is frozen, it will be in plate heat exchanger.
    In the same cooling system, there is 15 air cooler, working fine.
    Anyway, they said that according to pictures, it must be destroyed by frozen medium inside the cooler, and believe it or not, that warranty can not be accepted, and that we are free to order new cooler...

    Please see pictures enclosed, and please tell me that I am not crazy....

    Rio
    Last edited by Rio69; 23-06-2009 at 10:11 AM. Reason: accidently pushed enter too early



  2. #2
    Join Date
    Aug 2008
    Location
    Baltics
    Age
    62
    Posts
    786
    Rep Power
    16

    Re: Air cooler broken

    Hello Rio.
    But what might be your explanation of that burst(s) ? (as you hold incomparably more info about the system)

  3. #3
    Join Date
    May 2008
    Location
    Belgium
    Age
    66
    Posts
    802
    Rep Power
    16

    Re: Air cooler broken

    is it not possible that the mixing of the glycol and water occurd during the cooling process,whit running compressors?? if we start up a system whit a glycol mixture,we let it run for at least 12 Hrs whitout the compressor(s) running,so the mixture is allover the same quality.

    Ice

  4. #4
    Join Date
    Dec 2006
    Location
    Croatia
    Posts
    23
    Rep Power
    0

    Re: Air cooler broken

    It is an old system, where we added few coolers and are using existing mixture of glycol and water, which should be mixed well.
    I think it is manufacturing fault.
    It worked couple of days before burst.

    Rio

  5. #5
    Join Date
    Dec 2008
    Location
    Portugal
    Age
    48
    Posts
    1,020
    Rep Power
    19

    Re: Air cooler broken

    Hi Rio,

    I think the burst was caused by ice. The plate exchanger probably didn't burst because probably is a semiwelded type with gaskets which allow some ice expansion.

    The bends of the aircoolers are destroyed because in that location the ice cannot expand further.

    The mixture is 30% ethylene glicol in old times but probably with glycol leaks the Client only replace with pure water .

    I'm sorry man for what happen.

    Regards
    To make progress is never good enough, I want to do better and better and better

  6. #6
    Join Date
    Feb 2008
    Location
    adelaide sth.oz
    Posts
    1,015
    Rep Power
    19

    Re: Air cooler broken

    tend to go along with sandro rio had a stand buy pump on glycol and thought bearings where seized,stripped the stages and all i found was ice,probably not relevant to your situation,one would think that eveything works at time of commission.its been their for three years.thank the lord for keg rooms
    mmm to beer or not to beer...........lets drink breakfast

Similar Threads

  1. Cannot get the cooler to temp
    By coolrunnings1 in forum Fundamentals
    Replies: 13
    Last Post: 27-06-2009, 07:51 PM
  2. "Home made" ice water based packed food cooler
    By SteinarN in forum Fundamentals
    Replies: 2
    Last Post: 26-03-2009, 07:54 PM
  3. Cornelius "Pepsi" cooler power?
    By ibrubeer in forum Fundamentals
    Replies: 10
    Last Post: 01-09-2008, 10:51 PM
  4. TXV hunting in a walkin cooler
    By dkemper in forum Trouble Shooting
    Replies: 9
    Last Post: 15-11-2007, 03:14 PM
  5. Thermo-syphon Oil Cooler
    By B.B. in forum Industrial
    Replies: 5
    Last Post: 31-10-2005, 01:25 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •