23-06-2009, 06:09 AM #1
Ice formation on condensing coil of heat pump
can anybody tell me the reasons for ice formation on condensing coil of a heat pump running at low ambient temperature say 7 deg celsius.i checked the refrigerant charge & it is as per manufactures recommendation.
-
23-06-2009, 02:13 PM #2
Re: Ice formation on condensing coil of heat pump
What kind of heat-pump is this - AWHP - air-to-water?
Do you mean the 'evaporating coil', rather than 'condensing coil'?Engineering Specialist - Cuprobraze, Nocolok, CD Technology
Rarefied Technologies ( SE Asia )
-
23-06-2009, 11:17 PM #3
Re: Ice formation on condensing coil of heat pump
It's doing it's job of extracting heat from the ambient air.
That's why they have a defrost cycle.Brian - Newton Abbot, Devon, UK
Retired March 2015
-
24-06-2009, 12:19 AM #4
Re: Ice formation on condensing coil of heat pump
its an Aircooled APAC unit.Frost on the Condenser coil(Evaporater coil on heat mode) is just blocking the compressor start up.Please tell me all the possibilities for frost formation.
-
24-06-2009, 03:19 AM #5
Re: Ice formation on condensing coil of heat pump
Please tell me all the possibilities for frost formation.
Check the defrost cycle operation, as Brian mentions.Engineering Specialist - Cuprobraze, Nocolok, CD Technology
Rarefied Technologies ( SE Asia )
-
24-06-2009, 04:31 AM #6
Re: Ice formation on condensing coil of heat pump
Well there ya go, a heat pump doing its business,the out door coil will frost up even in Australia, if blocking compressor, sounds like a control issue.
magoo
-
26-06-2009, 09:59 PM #7
Re: Ice formation on condensing coil of heat pump
Blocking compressor?!?
The heat pump will have a defrost cycle on the system, most i've come across have a defrost stat, will defrost the coil at a set temperature.
Frost occurs because in 'simple terms' you are air conditioning your garden and dumping the heat generated to water, refrigerating air will rip the moisture out and inevitably frost up the 'cold' coil.
Check the drip tray and make sure its not blocked, overflowing water can cause frost problems with ice building up from the bottom of the coil, to check the defrost operation, try running the unit with the lid off, this will reduce the airflow over the Evaporator coil, should see the coil start to form ice and eventually knock out on defrost, depending on ambient temperatures.
-
27-06-2009, 09:10 AM #8
Re: Ice formation on condensing coil of heat pump
blocking compressor,
apacs have a defrost timer from 15-45 mins depending on which plug /bridge it is on. it gets ice on the coil because it is removing the moisture which is sticking to a cold coil. if it is running on heating are the filters clean?
-
01-07-2009, 12:14 AM #9
Re: Ice formation on condensing coil of heat pump
It maybe an idea to check the reistance of the thermistor & also was the humidity high outside.
-
01-07-2009, 04:27 AM #10
Re: Ice formation on condensing coil of heat pump
thank you all for your valuable suggestions.I have checked all these still persist the problem
-
01-07-2009, 04:58 AM #11
Re: Ice formation on condensing coil of heat pump
Is it actually running?
If so, is it going on it's defrost cycle or not?
APAC units have a sensor that's usually placed at the bottom of the coil, and connects to the main card at SEN1 & 2.
If any of the connections are corroded or loose, that could be your problem. Also, I've found that the sensor itself can get corroded & fail. Finally, is the sensor tight to the pipe?
How is the frost build up blocking the compressor from running?
-
07-07-2009, 06:22 AM #12
Re: Ice formation on condensing coil of heat pump
APAC particularly subject to faulting on low ambient start up ( suction dive with low temps) causing continual fault lock out during the winter that needs manual resetting. The units are a bit older but still other units of similar nature and capacity are working properly.
-
07-07-2009, 06:40 AM #13
Re: Ice formation on condensing coil of heat pump
A thought - the unit has probably lost a little refrigerant over time. Under the extreme cold start-up you're possibly getting a low-pressure trip as the compressor begins pulling hard.
The system can tend to pull down the suction pressure a lot on start-up. With low refrigerant charge, this can cause a LP trip. Check the LP trip setting, it may be set unusually high.Last edited by desA; 07-07-2009 at 06:51 AM.
Engineering Specialist - Cuprobraze, Nocolok, CD Technology
Rarefied Technologies ( SE Asia )
-
12-07-2009, 10:21 AM #14
Re: Ice formation on condensing coil of heat pump
This may help
Similar Threads
-
Calorex 510 Heat pump question
By jugglerb in forum Heat PumpsReplies: 8Last Post: 21-06-2009, 10:49 AM -
Sizing of Heat pump
By pinkpanther in forum Tools and CalculatorsReplies: 5Last Post: 24-05-2009, 08:16 PM -
Homemade Heat Pump...
By AC_Hacker in forum New to REReplies: 0Last Post: 29-04-2009, 11:30 PM -
Pool heat pump water side diagram
By nike123 in forum Heat PumpsReplies: 23Last Post: 22-03-2009, 07:42 PM -
Homemade Heat pump water heater
By busman in forum Technical DiscussionsReplies: 20Last Post: 05-02-2008, 04:04 PM