    Compressor Icing Up



    Hi all

    I was called to a unit not cooliong correctly today its a package on r22, now the evap is iced up right from the tev all the way back to the compressor and the compressor is iced up too,

    The filter was recently replaced and still clean so my first thoughts were low on gas, but with the compressor icing up now Im thinking maybe the tev is flooding the evap?

    Thanks in advance for any advice



  2. #2
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Compressor Icing Up

    Sounds like an airflow problem to me.

    There is a lot more to it. Check for blocked returns, dirty blower wheel, dirty coil, etc.

    With the coil defrosted, what are the evap air in/out temps (measured close to the coil)?
    Last edited by Gary; 22-06-2009 at 10:20 PM.

  3. #3
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Compressor Icing Up

    Compressor is icing because evaporator is iced and not picking up heat.
    Do not attempt to fiddle with charge or TEV until you defrost evaporator and undoubtedly establish that its air flow is as it should be.
    And finally, follow Gary's guidance.
    Last edited by nike123; 22-06-2009 at 10:57 PM.

  4. #4
    Join Date
    Mar 2009
    Location
    Mancheser
    Age
    41
    Posts
    55
    Rep Power
    16

    Re: Compressor Icing Up

    Ok, Thanks Guys I will get straight on it and let you know the outcome.

  5. #5
    Join Date
    Mar 2006
    Location
    Lancashire
    Posts
    1,859
    Rep Power
    28

    Re: Compressor Icing Up

    Did you check the superheat? You would know if you were getting liquid floodback to your compressor then.
    The difference between genius and stupidity is that genius has its limits.

    Marc

  6. #6
    Join Date
    May 2006
    Location
    India
    Age
    74
    Posts
    399
    Rep Power
    18

    Re: Compressor Icing Up

    May be evaporator has logged up with oil .

  7. #7
    Join Date
    Jan 2008
    Location
    north west
    Age
    42
    Posts
    234
    Rep Power
    19

    Re: Compressor Icing Up

    is it overcharged? is the tev ok?

  8. #8
    Join Date
    Mar 2009
    Location
    Mancheser
    Age
    41
    Posts
    55
    Rep Power
    16

    Re: Compressor Icing Up

    Right, I sripped it down and the evapourater looked a little dirty so I gave that a good clean with a cleaner and I checked the blower wheel, this had corroded quite bad and was causing a blockage between fins, (Thanks Gary) So I gave it a good scraping and blew it out with ofn.

    Seems to be running ok now and the air flow seems to have doubled!

    Must not of been hardly any air flow therefore evap not picking any heat up so no superheat back to the compressor.

    Cheers Guys