    a problem with a Bitzer two stage compressor,7.5HP: emits a very loud, high pitch noise when operating full capacity but runs normal at 50%.lubricating the solenoid valve initially helped,so did changing it-but the sound returned after some time.the capacity solenoid valve on the compressor head is definitively involved.any thoughts?



  2. #2
    Join Date
    Dec 2008
    Location
    UK
    Posts
    55
    Rep Power
    16

    Re: noisy compressor

    Hi, I believe the capacity control is acheived by Hot Gas Pressure being exerted on a piston, ie unloader valve.
    There is a "Teflon" seal on the piston and almost certainly a piston ring too. Should these be worn then I believe that possibly " Hot Gas " passing through a faulty seal or ring might cause the noise described by you. You will need to remove the unloader head and physically inspect the piston and cylinder of the unloader valve assembly. Good Luck.

  3. #3
    Join Date
    Dec 2008
    Location
    UK
    Posts
    55
    Rep Power
    16

    Re: noisy compressor

    Hi Again, I would also recommend you carry out an efficiency test on the compressor as you may find that the valve plate on the "Loader" cylinders has excessive wear causing the suction valves to "let by" discharge gas.

  4. #4
    Join Date
    May 2008
    Location
    Belgium
    Age
    66
    Posts
    802
    Rep Power
    16

    Re: noisy compressor

    hey centrecipew, would you discribe an efficienty test for comps pls.
    thnx, Ice

  5. #5
    Join Date
    Mar 2009
    Location
    Chicago, Il
    Age
    60
    Posts
    6
    Rep Power
    0

    Re: noisy compressor

    I may be wrong here but you cannot "unload" a Bitzer two stage compressor. You can false load it - which is not a good to stage design practice. Additionally, the "7.5" is a S4N-8.2 (aka 8HP) 4 cylinder. Two low stage cylinders pumping into the high stage side of which are smaller pistons. In my humble opinion, your high stage reeds are broke.

    To check - go to the BitzerUS site and download the software. Put in your conditions and check to see what you INTERSTAGE pressure is (shut off you subcooler feed). If its higher than the "modeled" interstage - its a high side issue..if its lower, it a low side issue.

    Good luck.

  6. #6
    Join Date
    Jan 2008
    Location
    newzealand
    Age
    47
    Posts
    44
    Rep Power
    0

    Re: noisy compressor

    From what you guys are saying yes, that is correct, also because your teflon seal is leaking past you will have a hike in suction pressure as well....

Similar Threads

  1. Help needed to find a replacement compressor
    By 540itouring in forum Domestic
    Replies: 19
    Last Post: 17-04-2010, 02:06 PM
  2. [Autocascade] Only a project ATM
    By before in forum CPU Overclockers
    Replies: 1
    Last Post: 07-05-2009, 11:13 AM
  3. Thumping noise in the compressor
    By Husky250 in forum Air Conditioning
    Replies: 6
    Last Post: 16-05-2008, 10:48 PM
  4. Compressor Knock problem
    By AC90 in forum New to RE
    Replies: 10
    Last Post: 11-05-2008, 04:26 PM
  5. screw compressor
    By vinod in forum Trouble Shooting
    Replies: 9