    Chilled water system design



    Help please
    I have to design a chilled water system which includes three chillers and three CRAC indoor units.
    The pipe and pump sizing is no problem and I know I need a buffer tank of 1000 litres.
    The question is; can I use the buffer tank as a feed/ expansion tank (fit a ball valve and mains feed) or do I have to have a seperate expansion vessel and if this is the case do I need a sealed buffer tank and a pressurisation unit which seems excessive as the system is quite small (150 kW). My thinking is that the water volume will expand and contract and this wil be accomodated by the buffer tank, the feed valve will top up if necessary or can the system use a manual fill as and when required?
    Thanks for your help



  2. #2
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Chilled water system design

    Buffer tanks do not contain any facility for expansion, i.e. membrane or air pocket. They are intended to smooth out the return temp to stop the chiller cycling un-necessarily. You need to fit an expansion vessel/pressurisation unit or manual fill

    If you go for the expansion vessel/manual fill option, I would install a pressure switch into the control circuit to hold the chiller off on loss of pressure.
    Last edited by frank; 22-06-2009 at 08:47 PM.

  3. #3
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Chilled water system design

    I would go for an ordinary feed and expansion tank.

    It's simple, cheap and does the job.

    Well that's what we did on the last chiller install; it also had a buffer tank.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  4. #4
    Join Date
    Aug 2003
    Location
    Netherlands
    Age
    49
    Posts
    620
    Rep Power
    21

    Re: Chilled water system design

    I would place the buffer vessel in the bypass line!

  5. #5
    Join Date
    Aug 2008
    Location
    UK
    Age
    62
    Posts
    8
    Rep Power
    0

    Re: Chilled water system design

    Thanks for the advice.
    I was planning to use an open/vented system with the chilled water flow from the chillers into a common primary circuit returning to the open buffer tank pump then back to the chillers, similar to a LPHW heating system. Is this possible of will the pump cavitate because the system is not pressurised?
    I have attached a schematic and would be very gratefull if youo can advise whether the proposed design will be ok.
    Thanks
    Attached Files Attached Files

  6. #6
    Join Date
    Aug 2003
    Location
    Netherlands
    Age
    49
    Posts
    620
    Rep Power
    21

    Re: Chilled water system design

    Here's a layout of a sound hydraulic layout for a chilled water system that works and can be controlled.

    In your design you'll have a variable flow through the chillers which is bad practice!
    Attached Files Attached Files

  7. #7
    Join Date
    Aug 2008
    Location
    UK
    Age
    62
    Posts
    8
    Rep Power
    0

    Re: Chilled water system design

    Thanks Lowrider
    Your design is the ideal solution but I inherited some of my layout and the pump quantity is fixed. The existing system had no buffer or expansion vessel just a F/E tank.
    As usual the client does not want to spend money so I plan to install regulating valves in each chiller return leg to try and equalise the flow.

  8. #8
    Join Date
    Aug 2003
    Location
    Netherlands
    Age
    49
    Posts
    620
    Rep Power
    21

    Re: Chilled water system design

    If you stick with that design you'll end up costing the customer more money! In order to get the right temperature from the chillers you'll have to run one at a much setpoint or have two running at very low load!

    With a well designed hydraulic layout one can safe in excess of 30% on energy!

Similar Threads

  1. Daikin fault codes
    By Chris2005 in forum Air Conditioning
    Replies: 45
    Last Post: 21-03-2012, 10:09 PM
  2. Leak Testing?
    By Thana in forum Trouble Shooting
    Replies: 36
    Last Post: 31-08-2010, 02:57 PM
  3. chart for PVC pipes closed chilled water system
    By mackistired in forum Air Conditioning
    Replies: 4
    Last Post: 14-11-2009, 03:23 AM
  4. Chilled Water A/C System.. antifreeze or no?
    By WangFu in forum Technical Speculations
    Replies: 17
    Last Post: 09-08-2007, 10:36 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •