Thread: cps vacuum gauge
-
22-06-2009, 11:32 AM #1
cps vacuum gauge
hello, i have a cps vg200 digital vacuum gauge and the readings are up the creek, it will only read properly if not connected to system. once the system is in a vacuum it just takes a lon time to register what micron it is reading. has anyone else seen or heard of this. thanks CT
-
22-06-2009, 12:31 PM #2
Re: cps vacuum gauge
Have you tried washing the sensor in alcohol or similar. May be oil contaminated.
-
22-06-2009, 11:39 PM #3
Re: cps vacuum gauge
Are you sure that the vacuum you have created is low enough to register on the gauge?
Also, as stated above, make sure that the sensor is clean and the battery is good.Brian - Newton Abbot, Devon, UK
Retired March 2015
-
24-06-2009, 08:57 AM #4
Re: cps vacuum gauge
hey guys
cleaned out with metho pulled vac pump down to 250 microns with dirty vac oil in pump.
thanks for your help guys
-
25-06-2009, 08:18 AM #5
Re: cps vacuum gauge
Hi, guys
Can anyone tell where I can buy pressure gauges, vacuum pump, recovery unit,..etc.. but not too expensive for a tight budget and somewhere here in London.
Thanks
-
25-06-2009, 08:58 AM #6
Re: cps vacuum gauge
local refrigeration dealer, i paid $330 aud for the vac gauge, $460 for a 120l/min vac pump. recovery unit about $900 aud. which is pretty good price for all
-
30-06-2009, 12:53 PM #7
-
30-06-2009, 01:37 PM #8
Re: cps vacuum gauge
Ah ha, another G.C-er! Welcome to R-E chillifive.
Sidi, I'd try fleabay. However remember you get what you pay for!
-
01-07-2009, 08:05 PM #9
Re: cps vacuum gauge
in Belgium we have a saying " goedkoop is niet altijd goeiekoop"...so translated it sounds " cheap bying isn't always best bying"
Ice
-
01-07-2009, 08:17 PM #10
Re: cps vacuum gauge
Had the same problem myself, connected up the vac pump and stared pulling a vac, next the gauge stops working. Vac pump had pulled out oil mist from the system and contaminated the sensor. Now i vac systems for an hour befor fitting the guage, no more failures.
ice/ruuner
-
01-07-2009, 10:47 PM #11
Re: cps vacuum gauge
^ Also, vac guage shouldn't be fitted to vac pump; it should be connected directly to the system if possible.
Brian - Newton Abbot, Devon, UK
Retired March 2015
-
03-07-2009, 01:18 AM #12
Re: cps vacuum gauge
And also as far on the system from the vac pump connection as you can get.
Similar Threads
-
Sticky Imperial hp pressure gauge
By desA in forum Trouble ShootingReplies: 12Last Post: 21-04-2009, 03:03 PM -
Troubleshooting a vacuum pump and gauge set.
By Old Codger in forum FundamentalsReplies: 7Last Post: 08-08-2008, 05:13 PM -
Evacuation Procedure Electronic Vacuum Gauge
By Refrigerologist in forum CommissioningReplies: 30Last Post: 14-04-2008, 12:34 AM -
inverters pulling vacuum
By bangoman in forum Air ConditioningReplies: 2Last Post: 05-02-2008, 09:12 PM -
Vacuum test
By Peter_1 in forum FundamentalsReplies: 15Last Post: 13-10-2006, 09:04 PM