Hi dear members,
I have joined this forum recently.
Can anybody tell the maximum/ minimum allowable superheat & suction gas temperature recommended for single stage R-22 sealed compressors for air-conditioning applications. To be specific the compressor in question is Bristol H2BG094DBE.
Please provide relevant web resources/ manufacture recommendations/ applicable standards for reference.
Thanks,
-
22-06-2009, 07:17 AM #2
Re: Maximum allowable Superheat
Have a search on here http://www.bristolcompressors.com/
-
22-06-2009, 12:29 PM #3
Re: Maximum allowable Superheat
For fixed metering I would say you could be anywhere from 10 to 33F. it depends on the actual load and the outdoor temperature
When it is cool out, there is a lower condensing temperature so less head pressure pushing refrigerant through the metering device and hence high superheat as the evap coil is somewhat starved.
As it gets warmer out , the condensing pressure will go up and this pushes more refrigerant through the metering device and this tends to push the superheat down.
However as it gets warmer out, it tends to get more humid out.The infiltration into the space tends to elevate the wet bulb somewhat and this increases load on the evaporator and pushes superheat up.
So with fixed metering it is a range of superheat that can be deemed normal, you really need to look at subcooling at the same time to assess the charge.Take the V out of HVAC and you are left with a HAC job
-
23-06-2009, 06:22 AM #4
Re: Maximum allowable Superheat
Dear Abby Normal
The unit has installed a TXV to control the superheat of the system. However, the superheat is found more then 20F i.e. around 30-35F, whereas subcooling is around 18-25F.
-
23-06-2009, 06:42 AM #5
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
Re: Maximum allowable Superheat
Last edited by nike123; 23-06-2009 at 06:44 AM.
-
23-06-2009, 01:11 PM #6
Re: Maximum allowable Superheat
I would say with 30 to 35F superheat with a TX valve that you either have a very big load on the system, more than it can handle or your TX valve is undersized, it is wide open and there is not enough head pressure available to push enough liquid through the wide open valve and the evaporator coil is getting starved.
It also sounds like someone has givien it extra refrigerant as well to try and compensate.
It could also have some junk in the system clogging what enters the TX valveTake the V out of HVAC and you are left with a HAC job
Similar Threads
-
9 superheat & subcooling scenarios
By nike123 in forum FundamentalsReplies: 39Last Post: 19-07-2011, 03:16 AM -
Superheat and Subcooling
By Chunk in forum FundamentalsReplies: 42Last Post: 15-01-2011, 01:24 AM -
Carrier 23xl chiller-Low discharge superheat alarms